I'd stay away from locating a sprinkler above the bar type bathroom lights. 
They can put out quite a lot of heat, and we all know what goes up...
This sounds like a residential fixture, if so, the bulbs may be replaced later 
with a higher wattage creating more heat.  

Jamie
Sent from my iPhone

On Sep 24, 2010, at 3:48 PM, "A.P.Silva" <[email protected]> wrote:

> 
> 13, 2007 table 8.3.5.2(c) gives minimum distance from edge of 0 W to 250 W
> light fixture to 155 deg.F sprinkler as 6 inches. In what direction is this
> measurement taken? 
> 
> If both sprinkler head and light fixure are mounted on a ceiling there is no
> problem, as it will be the closest horizontal distance. Is it still the
> horizontal distance when they are on a different plane?
> 
> My situation is: A sidewall sprinkler mounted on a bathroom wall, 6" below
> the ceiling is 10" directly above a four bulb x 60 W (total 240 W)wall
> mounted light fixture. Is this acceptable?
> 
> Tony 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Gregory
> Lindholm
> Sent: September 24, 2010 10:21 AM
> To: SprinklerFORUM
> Subject: Seed corn in plastic totes
> 
> 
> 
> I have a customer that is looking to build a building with 30' eaves,
> storing seed corn in 4' x 4' x 3' high (open top) plastic totes, stacked as
> high as possible (over 30' high at the peak).
> 
> Dry systems, so no ESFR.
> 
> We are coming up with Group A plastics, but it looks like the highest that
> they could stack is 25'.
> 
> What are we missing, or what are forum members thoughts?
> 
> Greg Lindholm
> 
> 
>                         
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to