Dear colleagues,

A client has a truck loading building where tankers are filled with combustible (edible) oil. The building is protected by a foam/water sprinkler system according to NFPA 13 & 16.

There are a few skylights, distributed over the roof of the building. Spacing between the skylights exceeds 10 ft (3 m). The area of each skylight exceeds 32 ft2 (3 m²).
The skylights have plastic covers.
The bottom of each skylight is closed with a transparant plastic panel that flattens out the bottom of the skylight with the surrounding ceiling. The plastic cover on top and the plastic panel at the bottom create inside the skylight a concealed space with a height of approx. 2 or 3 ft.

The roof is covered with non-combustible ceramic insulation (rockwool) and bitumic sheeting on top of it.

Question: are sprinklers required in these skylights? What is your opinion?


Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to