Blow up the HVAC unit?, just ;)

Locate the head with deflector at bottom of the 16" deep obstruction. Show
the section where head can be located up to 22" for obstructed construction.

Tony  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: November 1, 2010 3:01 PM
To: [email protected]
Subject: RE: Mechanical closet obstruction

Existing condition. Not going to happen


At 04:43 PM 11/1/2010, you wrote:
>It may be hard for him to shove the HVAC unit against the wall. With 
>the minimal space allowed in this closet he still needs room to make 
>duct connections, electrical connections, drain connections etc.  But 
>hey you could ask.
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of 
>[email protected]
>Sent: Monday, November 01, 2010 4:25 PM
>To: [email protected]
>Subject: RE: Mechanical closet obstruction
>
>Todd,
>This is just a thought.Get the HVAC contractor to shift the unit into 
>the corner,then place the sprinkler in the opposite,leaving 8" clear on
>2 sides.You can maintain the 4" min. off the wall and cover ALL the 
>clear space in the room.Right?
>
>Lamar Vaughn
>
>
>On Mon, Nov 1, 2010 at 2:53 PM, Todd Williams wrote:
>
> > This is under the 2002 code and they have the 5 ft ceiling height 
> > restriction. I believe this is an 8 ft ceiling.
> >
> >
> >
> > At 02:28 PM 11/1/2010, you wrote:
> >> Todd,
> >>
> >> If this is residential, 6.8.1.5.3.1 specifically addresses this 
> >> concern.
> >> 2007 ed.
> >>
> >> Cliff
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Todd 
> >> Williams
> >> Sent: Monday, November 01, 2010 1:22 PM
> >> To: [email protected]
> >> Subject: Mechanical closet obstruction
> >>
> >> I know this was referenced in another post, but I can't find it so 
> >> I'm starting a new thread.
> >>
> >> A 2' x 2' mechanical closet. The unit is mounted on the floor and a 
> >> 16" x 16" plenum comes off the top and runs up through the ceiling 
> >> at roughly the center of the room (approximately 4" clearance on 
> >> each side). One sidewall sprinkler is installed near the ceiling 
> >> and the AHJ questions the head being obstructed. Outside of 
> >> installing 4 sprinklers in the closet, any good way to address 
> >> this? The State Building Code specifically excludes the application of
common sense.
> >> Thoughts?
> >>
> >> Todd G. Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, CT
> >> 860.535.2080
> >> www.fpdc.com
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: 
> >> [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: 
> >> [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]
> >> (Put the word unsubscribe in the subject field)
> >
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > 860.535.2080
> > www.fpdc.com
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: 
> > [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field) 
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to