This woke me up at 3:00 A.M.- it has error written all over it- I apologize
to the Forum, and vow to double check my numbers AND my motives before I
post anything. In terms of density vs fire power with little heads flowing a
minimum:
5.4 gal/min x 3.781 liter/gal/60= .3403 Kg/sec x 4,180 Kj/Kg= 1,422 Kw/500
Kw/tree= 2.84 big dry Christmas trees, not 6, and now I have to perish the
thought that one head in this closet seems inadequate somehow :)

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Tuesday, November 02, 2010 7:51 AM
To: [email protected]
Subject: RE: Mechanical closet obstruction

Todd, maybe some words and numbers together would work, e.g., "We put water
on floors. An obstruction is something that prevents the water from reaching
every square foot with a minimum density". 2 strips at 4"x24" + 2 @
4"x16"=320/144=2.2 SF. (dbl chk 4-1.8=2.2) Maybe the head is just a 4.2 so
Q=12/2.2=5.4. This is a pretty decent density (36 X min).
12x3.781=45.372/60=.756 Kg/sec x 4,180 Kj/Kg/sec= 3,161 Kw/500 Kw/tree.
(Pardon my French with the numbers). It is not every day we get to give the
AHJ a density that could handle the fire power of 6 big dry Christmas trees
at peak burning rate with little heads flowing a minimum.