Globe allows something I think, but it's more along the lines of
meeting the slope when 2:12 or less. Check their manual.

On Wed, Dec 1, 2010 at 7:11 AM, Cliff Whitfield <[email protected]> wrote:
> Duane,
>
> I don't think so.  You would need to defer to the sprinkler manufacturer's
> listing to be sure.
>
> Cliff
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dewayne
> Martinez
> Sent: Wednesday, December 01, 2010 8:48 AM
> To: [email protected]
> Subject: QR HSW in 13R residential dwelling unit
>
> Can you ignore the deflector orientation rules for NFPA 13
> when using a QR HSW sprinkler in a NFPA13R building?
> IE:  Throw across a 4/12 pitch slope?
>
> I don't think so but 13R (07ed) 6.7.7.3 doesn't specifically
> address deflector orientation so maybe?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to