Remember that for standard coverage HSW sprinklers, NFPA 13 requires 
installation at the highest point discharging down the slope.  There is no 
listing deviation from the standard that I am aware of.  For slopes greater 
than 2/12 pitch, EC and residential sprinklers must be listed to discharge 
across the slope.  In all cases, deflectors must be parallel with the slope.

Regards,

Salvatore Izzo PE SFPE
Manager-Reliable Technical Services
------Original Message------
From: Dewayne Martinez
Sender: [email protected]
To: [email protected]
ReplyTo: [email protected]
Subject: QR HSW in 13R residential dwelling unit
Sent: Dec 1, 2010 9:48 AM

Can you ignore the deflector orientation rules for NFPA 13
when using a QR HSW sprinkler in a NFPA13R building?
IE:  Throw across a 4/12 pitch slope?
 
I don't think so but 13R (07ed) 6.7.7.3 doesn't specifically
address deflector orientation so maybe?