OK, I stand corrected.  The plumber that prepared the FP specs did not know
which boxes to click from their master spec writing software.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-----Original Message-----
From: Jeff Hewitt [mailto:[email protected]] 
Sent: Monday, December 20, 2010 3:24 PM
To: '[email protected]'
Subject: RE: @#*% Hose Stations

If this is not a design-build project, and the specs do not require them,
even though the AHJ does, then I agree, the plumber that wrote the FP specs
blew it.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Monday, December 20, 2010 2:55 PM
To: [email protected]
Subject: @#*% Hose Stations

I know this is a no brainer but any help would be appreciated. We are doing
a warehouse system with ESFR heads, shop drawings were approved by all
parties, Architect, Engineer, AHJ. The only comment was from the AHJ that
stated he wanted (3) hose stations added, no big deal. We send the GC a
change order for the addition of the hose stations and it gets approved; now
the GC wants us to provide additional information as to why we didn't
include hose station in our original bid. We explained that there were no
hose stations shown in the contract drawings or in the spec's and that
NFPA-13 doesn't require them. Apparently the owner is trying to get the GC
to pay for them because he didn't consult his crystal ball when he bid it
and should have seen that the AHJ was going to add them! I know we're clean
from our end but was just trying to help the GC out, any ideas?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16540)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________