Sean,

The remote test connection is only required for dry systems in order to 
determine that water will reach the most remote point in the allotted time.

Tim Frankenberg, CT, CFPS
Fire Product Manager
Potter Electric Signal Company LLC
5757 Phantom Drive, Suite 125
Hazelwood, MO 63042
800-325-3936
www.pottersignal.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Tony Liddic
Sent: Friday, January 14, 2011 1:16 PM
To: [email protected]
Subject: RE: Code reference for replacing remote end inspectors test with 
alisted Test N' Drain Valve....

Sean,

The 2002 Handbook says the following after 8.16.4.2.3:

"Ideally the inspector's test connection is located at the end of the most
remote branch line in the upper story.  Such a location is not, however,
required.  For a wet pipe system, the exclusive purpose of the inspector's
test is to verify operation of the alarm attachment, which is the reason
that the test connection is not mandated at the remote portion of the
system.  The test connection is only required to be located downstream of
the alarm device."


Tony Liddic, CET
MRH Sprinkler Design LLC
356 Laurel Glen Dr.
Springboro, OH  45066
937-369-7926
http://www.mrhsprinklerdesign.com
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sean Lockyer
Sent: Friday, January 14, 2011 1:44 PM
To: [email protected]
Subject: Code reference for replacing remote end inspectors test with a
listed Test N' Drain Valve....

Does anyone know the specific code reference from NFPA 13, 2002 Edition,
that allows for the deletion of the remote end inspectors test when you use
a test and drain valve on the riser (Such as an AGF).

I found it once but I'm having a heck of a time finding it again...

Any help would be great appreciated as I would be in your debt...

--
Sean Lockyer
Project Designer
Delta Fire Sprinklers
(407) 328-3000, ext 139
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to