One thing to consider if the ITV is at the flowswitch instead of at a remote 
location is trapped air.
If there isn't a vent or remote valve that can be opened when filling, then all 
of the air that is in the empty system has no where to go when you begin 
filling.
This air will compress as the water enters, building up system pressure until 
the Back Flow Preventor closes even though the system is only partially filled 
with water.
This trapped compressed air can cause multiple problems including increased 
oxygen corrosion, cycling of the flowswitch when testing and/or delayed 
operation of the flowswitch.
When the ITV is opened the compressed air pushes system water out of the test 
valve. 
When the pressure drops enough the BFP will open allowing supply water to flow 
in and start the flowswitch retard. 
Since the system is not full of water, more water is flowing in than what can 
flow out of the ITV. This compresses the air again building up pressure until 
the BFP closes.
Supply water stops flowing in allowing the flowswitch to reset.
The compressed air pushes system water out of the ITV until the pressure drops 
and the whole cycle starts over again.
There will be a steady stream of water flowing out of the ITV but there is not 
a steady stream of supply water flowing past the flowswitch.
The flowswitch cycles back and forth. The flowswitch will either go in and out 
of alarm or may not go into alarm at all depending on the length of cycles and 
retard time.
Leaving the ITV open for a long time doesn't help much because most of the air 
works towards the top of the system.
Setting the retard for a shorter time delay doesn't help because opening the 
ITV bled of any excess pressure that may have built up and a prolonged increase 
in supply pressure such as the city turning on pumps early in the morning to 
meet the demands of the day can create a surge long enough to overcome the 
retard and cause a false alarm.

I'm not saying the ITV shouldn't be installed at the flowswitch, I know it 
saves time and money for installation & testing. I'm just saying that there 
should also be a vent, either manual or automatic to vent off the air as the 
system is being filled to aid in the reduction of oxygen corrosion and cycling 
or delayed flowswitch operation.

Sorry to be so wordy but we receive calls about this on a regular basis.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740 Direct
www.pottersignal.com
 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Friday, January 14, 2011 2:40 PM
To: [email protected]
Subject: RE: Code reference for replacing remote end inspectors test 
withalisted Test N' Drain Valve....

True, but the latest editions are very clear that it is not required nor even 
recommended to locate the ITV at the most remote portion of the system:

NFPA 13, 2010 
8.17.4.4        The alarm test connection shall be permitted to be installed in 
any location on the fire sprinkler system downstream of the waterflow alarm.
A.8.17.4.2      (Partial second paragraph) "... Putting the test connection at 
the most remote portion of the system causes the introduction of fresh oxygen 
into a large part of the system each time the alarm is tested and increases the 
corrosion that will occur in the piping."

The prevailing attitude has changed significantly since the 2002 edition.  On 
top of that, here in Southern California (as in other areas of this state, and 
some areas in other states) we have to contend with stormwater pollution 
prevention regulations that now strictly preclude and prohibit sprinkler 
discharge onto hard surfaces that will run toward, or directly into storm drain 
systems.  It is much easier to coordinate a floor sink or hub drain at the base 
of the riser, into which we can dump both alarm test and main drain discharges, 
than to deal with the routing and accessory sanitary sewer connections that 
come with remote test locations.

Steve 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Tony Liddic
Sent: Friday, January 14, 2011 11:16 AM
To: [email protected]
Subject: RE: Code reference for replacing remote end inspectors test with 
alisted Test N' Drain Valve....

Sean,

The 2002 Handbook says the following after 8.16.4.2.3:

"Ideally the inspector's test connection is located at the end of the most
remote branch line in the upper story.  Such a location is not, however,
required.  For a wet pipe system, the exclusive purpose of the inspector's
test is to verify operation of the alarm attachment, which is the reason
that the test connection is not mandated at the remote portion of the
system.  The test connection is only required to be located downstream of
the alarm device."


Tony Liddic, CET
MRH Sprinkler Design LLC
356 Laurel Glen Dr.
Springboro, OH  45066
937-369-7926
http://www.mrhsprinklerdesign.com
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sean Lockyer
Sent: Friday, January 14, 2011 1:44 PM
To: [email protected]
Subject: Code reference for replacing remote end inspectors test with a
listed Test N' Drain Valve....

Does anyone know the specific code reference from NFPA 13, 2002 Edition,
that allows for the deletion of the remote end inspectors test when you use
a test and drain valve on the riser (Such as an AGF).

I found it once but I'm having a heck of a time finding it again...

Any help would be great appreciated as I would be in your debt...

--
Sean Lockyer
Project Designer
Delta Fire Sprinklers
(407) 328-3000, ext 139
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to