Yes I did drop a decimal place, thanks to those that pointed that out. 

But in answer to the last post, it doesn't matter if you're in TX or AK if
your drum drip is full of water and freezes it can break, no matter 2" or
1".

If you follow the 13 example, the bottom of the DD is a 1" nipple and valve
with a plug. That 1" nipple can freeze no matter if it's 6" long or 6'-0"
long if it's full of water and freezes long or hard enough. That's not to
say that a 2" nipple couldn't freeze, it just takes a little (very little)
while longer.