I know that if it is combustible and the FP System is per NFPA #13 the hair we 
are splitting is if it is LH or OH but, wouldn't whether it is considered a 
story or not be something decided by the architect and the local building 
department? If the plans call it an attic or don't call it anything at all and 
it's not calculated as part of the total square feet of the building then it 
should be an attic. By calling the attic a an occupied space a three story 
building with an accessible attic would be 4 stories and require a standpipe 
system.


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thom
Sent: Thursday, January 20, 2011 9:54 AM
To: [email protected]
Subject: RE: DEFINITION OF A CONCEALED SPACE

The space you describe meets the definition of a Story as described in
Chapter 2 of the IBC 2009. Additionally, 302.1 of IBC 2009 say's "A room or
space intended to be occupied at different times ---- "
With a door, how can it be a concealed space. Even a locked door does not
create a concealed space, just one with limited access. The fact that the
roof goes to 0'-0" at the eaves, only means that there is not true wall,
similar to the ever popular A-frame.

I say you've got a "Room", determine the occupancy and provide appropriate
protection as required by the applicable standard.

My farthing's worth.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Wednesday, January 19, 2011 8:19 PM
To: [email protected]
Subject: DEFINITION OF A CONCEALED SPACE

Is a large are with a concrete floor, exposed roof trusses with a door 
for access so the area can be utilized as a room (for storage 
presumably), considered a room or a combustible concealed space?

Peak height 10-0 and eaves go to zero.
Thanks for quick answers,
Greg
-- 
Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road 
Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to