As long as we're splitting hairs, if your "System after surge pressure was
110 Psi but you heads on arm overs where located more than 24'-0" above the
gauge location, you wouldn't have an operating pressure, or static pressure
of over 100 Psi.

As I said "Splitting hairs"

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, January 20, 2011 2:22 PM
To: [email protected]
Subject: Re: Hangers and pressure surges

And if the trapped surge pressure was over 100# but the overall
pressure was not you would already have a static exceeding 100 and
need the hanger anyways. If you then release a head anywhere in the
system you won't have a sudden momentary increase in pressure but an
immediate drop towards residual. That is: 1. That I'm understanding
the question, or 2. that we're still on planet Earth.

On Thu, Jan 20, 2011 at 12:28 PM, Roland Huggins
<[email protected]> wrote:
> I don't believe it was the intent to apply the requirement to the possible
> build-up of pressure from surges but to the actual available supply.  The
> definition in 3.3.19 does state exclusive of surges.  Combined with the
new
> expansion of requiring a relief valve on all wet pipe systems instead of
> just gridded systems (7.1.2.1 2010 ed), says to me that it's the
> characteristics of the  water supply that drive the requirement.
>
> Roland
>
>
> On Jan 20, 2011, at 11:20 AM, Sam Kassab wrote:
>
>> The pressure relief seems like the best option in this case.
>>
>> Thanks for the feedback.
>>
>> Sam Kassab
>> TridenT FIRE PROTECTION, INC.
>> 13631 Pawnee Rd. , Suite A-1
>> Apple Valley, CA 92308
>> Tel :   (760) 961-7222
>> Fax :  (866) 501-5942
>> Cell:  (805) 801-4676
>> Lic.  C-16 935502
>> [email protected]
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Chris
>> Cahill
>> Sent: Thursday, January 20, 2011 11:12 AM
>> To: [email protected]
>> Subject: Re: Hangers and pressure surges
>>
>> The issue is most problematic when the head first pops.  So I think the
>> AHJ
>> has a point.  Oh and 9.2.3.4.4.1 seems to actually support the AHJ
legally
>> where it clearly says static or flowing.
>>
>> Now if your real static without surge is below 100 you have the option of
>> controlling surges instead or changing hangers as I would interpret.
>>
>> Chris
>> -----Original Message-----
>> From: "Sam Kassab" <[email protected]>
>> Sender: [email protected]
>> Date: Thu, 20 Jan 2011 10:46:49
>> To: <[email protected]>
>> Reply-To: [email protected]
>> Subject: Hangers and pressure surges
>>
>> NFPA requires hangers to be installed on armovers over 12" when operating
>> pressure is over 100 PSI.  What if normal street pressure is below 100
PSI
>> and pressure surges cause a build-up of 100 PSI or more on the system
side
>> of the check valve?  The AHJ's argument is that the system will have over
>> 100 PSI when the system first operates, albeit for a brief moment.  Is
the
>> AHJ correct in his interpretation of this requirement?  Has anyone ever
>> come
>> across this question?
>>
>>
>>
>> Thanks in advance.
>>
>>
>>
>> Sam Kassab
>>
>> TridenT FIRE PROTECTION, INC.
>>
>> 13631 Pawnee Rd. , Suite A-1
>>
>> Apple Valley, CA 92308
>>
>> Tel :   (760) 961-7222
>>
>> Fax :  (866) 501-5942
>>
>> Cell:  (805) 801-4676
>>
>> Lic.  C-16 935502
>>
>> <mailto:[email protected]> [email protected]
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to