I read exactly what Mike said in those lines. If it supply path is to a sprinkler only it needs toe listed. If the supply path is to a sprinkler with plumbing along the way it needs to be listed and it also needs to comply with all the plumbing stuff.. If the path is solely to a plumbing fixture it needs only comply with plumbing stuff. You can't downgrade sprinkler requirements because the sprinklers come off a plumbing system any more than you can use non-potable pipe for the sprinklers that are supplied from the plumbing system with backflow protection or the like separation.
On Wed, Jan 26, 2011 at 2:50 PM, <[email protected]> wrote: > Herb; 2007 Edition see > > 6*3 condition 3. . . Piping connected to the system that supplies only > plumbing fixtures complies with local plumbing and health authority > requirements but is not required to be listed. > > 2010 Edition see 6.3.3.1 (same text as above.) > > 6.3.3 All piping in the system supplying sprinklers shall be listed and > conform to piping specifications of this standard. > > This is the same as condition 2 in 2007 > > My note: not an official interpretation of a committee member bla bla > disclaimer required because I was a committee member in 2010 cycle > > Everything before the sprinklers must be listed. Only piping off the system > to a fixture can be not listed by UL or other lab. (And plumbing pipe and > fittings and sprinklers must have NSF approval for potable water.) > > Hope this helps. My internet is down so I had to send this with my phone > sorry. > > Nice to hear from you. > > Mike Cabral > > > Sent on the Sprint® Now Network from my BlackBerry® > > -----Original Message----- > From: "Herb" <[email protected]> > Sender: [email protected] > Date: Wed, 26 Jan 2011 14:13:03 > To: <[email protected]> > Reply-To: [email protected] > Subject: RE: 13D Multipurpose Inspection > > Mike > It's been a while since we've talked. I have come across some interesting > stuff lately regarding multipurpose systems and wanted to run it by you. > > I have plumbers and the mfg rep from Uponor telling me that it is perfectly > legal and acceptable to install a normal domestic plumbing system using non > listed PEX pipe and non UL listed (1821) fittings and tie it into the > sprinkler heads. They say the way they read the code (they haven't been > able to identify the code number yet) as long as the fitting with the > sprinkler is listed, the 'T' off the plumbing system is listed, and the PEX > in between is listed they are legal and conforming to code. This seems > wrong to me. It defeats the purpose of requiring the fire sprinkler system > to be composed of UL 1821 listed components if 95% of the pipe and fittings > between the incoming water and the sprinkler system is not listed for fire. > > Comments? > > Herb Schairbaum > Blue Water Fire Sprinklers > 253-279-3603 > 253-927-8781 Fax > [email protected] > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)