Maybe scroll through this from January 2010?

You're correct Ron.  Biggest reasons for not sprinklering is either fear of 
accidental head discharge and/or electrocution from the accidental head 
discharge.  Neither can be substantiated through verifiable statistics.

Last year I did some investigation of reported Industrial accidents related to 
electrocutions and the only fire fighter electrocution recorded for the past 
15+ years was for a wildfire where a power line fell into an area where 
firefighters were using a hose attack.  There was not one recorded incident of 
ANY personnel being injured due to water in an electrical room.  

The perception is that sprinklers randomly discharge all the time, all 
sprinkler systems are deluge systems, if someone is standing in the room when 
the sprinklers discharge they could be electrocuted.

Typically dry equipment isn't as great a risk as oil filled, but still a risk.

We had a carpet warehouse locally that had a fire begin in their second floor 
electrical room.  Fortunately it was sprinklered.  The fire was out before the 
FD arrived.  This place stored millions of dollars of imported rugs.  When the 
news report stated the sprinkler saved the building, it was like "YES, Score 
one for the sprinklers."  They reopened the store later that day.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Tuesday, January 05, 2010 10:39 AM
To: [email protected]
Subject: Re: Electrical Rooms

Addressing Craig's mention of perceptions. There is a horrendous fear of water 
damage among most (and especially electrical) engineers. I once had an 
electrical engineer tell me you couldn't sprinkler a hydro-electric plant. 
First because it was too full of electrical equipment and secondly (and more 
humorously) because there wasn't enough water. When I pointed out that he had 
the second biggest river in North America backed up against one side of his 
building he told me that you couldn't use that water. I tried to find one of 
those tables like in 13D as to where fires most commonly start in commercial 
buildings but ran out of time. My gut tells me electrical rooms could be a 
prime location and electrical vaults (where the transformers are) also seem to 
be culprits. I just don't have any numbers to back up MY perceptions so will 
not try to enforce them.

On Tue, Jan 5, 2010 at 7:26 AM,  <[email protected]> wrote:
> It makes no difference whether the line passes through the room or comes in 
> and stops as long as you are in the allowable space as defined within the 
> section of the electrical code.  People are extrapolating limitations based 
> on their perception not on code verbiage.  We've had several detailed 
> discussions on this matter.
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
> 864.599.8439 [email protected] http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Tuesday, January 05, 2010 9:44 AM
> To: [email protected]
> Subject: Re: Electrical Rooms
>
> In the handbook of NFPA 72 they show a figure where the sprinkler pipe ends 
> in the electrical room , but it does not go thru the room.
> mario berrios
>
>
> -----Original Message-----
> From: George Church <[email protected]>
> To: [email protected]
> Sent: Mon, Jan 4, 2010 11:54 am
> Subject: RE: Electrical Rooms
>
>
> Remember they're the ones finding the invisible fault with you 
> crossing an electrical room with your piping.
>
> So that you are sure you comply FULLY with the applicable code 
> preventing you from doing this (ITHO) ask them to provide the 
> applicable code reference.
>
> glc
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Eladio N.
> Alvarado
> Sent: Monday, January 04, 2010 11:38 AM
> To: [email protected]
> Subject: RE: Electrical Rooms
>
> Eric:
>
> I understand and agree with you, but the EOR insist that the 4" main 
> to the FD Connection, which by the way is dry (check valve in another
> space) should not cross the room since is in violation of NEC, 
> according to their interpretation. I have already recited chapter and 
> verse of the code requirements and exceptions, but it doesn't seem to 
> sink in. There may other issues that affect their perception or 
> attitude, but I'm kind stuck, and would really like to find 
> irrefutable proof to my point.
>
> Eladio Alvarado
> AFSDII
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]]On Behalf Of Eric 
> Tysinger
> Sent: Monday, January 04, 2010 10:37 AM
> To: [email protected]
> Subject: RE: Electrical Rooms
>
> To my knowledge, there is nothing from NFPA 13 that addresses this. 
> The clearance requirements are found in the NEC, and there is nothing 
> in the NEC that prohibits piping from entering and exiting the 
> electrical room.
> Don't
> forget there are rules in NFPA 13 that allow the sprinkler to be 
> omitted. I try to use these to avoid the questions all together.
>
> Thanks,
> Eric Tysinger CET
> NICET 108988
> Designer
> Wayne Automatic Fire Sprinklers, Inc.
> 4370 Motorsport Drive
> Concord, NC 28027
> p: (704)782-3032
> f: (704)795-6838
> C: (239)633-9703
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Eladio N.
> Alvarado
> Sent: Monday, January 04, 2010 9:31 AM
> To: [email protected]
> Subject: Electrical Rooms
>
> Happy New Year to all!!
>
> I know that we have previously discussed Electrical Equipment rooms, 
> and that the general consensus is that there is nothing in NFPA 13 
> that prohibits sprinkler pipe, be it mains and/or branch lines from 
> entering the room, as long as it doesn't violate the require perimeter 
> area of the particular equipment. Now my question is; is there a 
> technical interpretation from NFPA 13 that explains this, and that 
> someone in the forum may be aware of? I could really use this info to 
> nail this subject closed with the EOR.
>
> Thanks in advanced,
>
> Eladio Alvarado
> AFSDII

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Thursday, January 27, 2011 2:59 PM
To: [email protected]
Subject: RE: Electrical Rooms

C'mon man!

Brian Harris
FDFP Inc.
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike
Hairfield
Sent: Thursday, January 27, 2011 2:54 PM
To: AFSA SprinklerFORUM
Subject: RE: Electrical Rooms


This is Lazy, look it up in the NEC
 
> From: [email protected]
> To: [email protected]
> Subject: Electrical Rooms
> Date: Thu, 27 Jan 2011 14:47:30 -0500
> 
> I'm being lazy but does anybody know off the top of their head if you can
> run sprinkler lines over an Electrical room if it has a ceiling?
> 
> 
> 
> Thanks!
> 
> 
> 
> Brian Harris
> 
> First Defense Fire Protection
> 
> 11957 Ramah Church Road
> 
> Huntersville, NC 28078
> 
> Phone: 704.948.3506
> 
> Fax: 704.948.3507
> 
> Nicet # 128476
> 
> 
> 
> 
> 
> 
> 
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to