And it's the electrical code.  We get comments and RFI's all the time that 
assume the electrical code prohibits piping from passing through electrical 
rooms.  What the code says is to keep piping out of the "Dedicated Space" above 
equipment, all the way up to the deck or to below a rated ceiling.    

SML



Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Brad Casterline" <[email protected]>
Sender: [email protected]
Date: Thu, 27 Jan 2011 14:53:02 
To: <[email protected]>
Reply-To: [email protected]
Subject: RE: Electrical Rooms

Stay out of the air space from the top of all panels up bcoz that is where
the conduit is and your pipe won't fly there
-----Original Message-----
From: Brian Harris [mailto:[email protected]] 
Sent: Thursday, January 27, 2011 1:48 PM
To: [email protected]
Subject: Electrical Rooms

I'm being lazy but does anybody know off the top of their head if you can
run sprinkler lines over an Electrical room if it has a ceiling?

 

Thanks!

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to