We've always concealed them in a soffit or perpendicular wall.  As long as the 
insulation is at the exterior wall you'll be fine.  Not really sure where he is 
coming from with that.  You are still within the heated envelope of the 
building.

Jamie
Sent from my iPhone

On Feb 21, 2011, at 5:53 PM, "Travis Mack, SET" <[email protected]> wrote:

> How is everyone installing these heads when req'd?  One of my customers just 
> left a meeting with the Tyco Rep and he was told that you were required to 
> have x" of dry barrel exposed (depending on temperatures) in the room, and 
> that it could not be concealed in a soffit or decoshield.  We can't see some 
> of these high end apts or condos allowing 4-6" of exposed dry barrel in a 
> unit.  What are others in cold climates doing with these situations?
> 
> -- 
> Please feel free to call if you have any questions or comments.
> 
> Sincerely,
> 
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> Office (480) 505-9271
> Fax (866) 430-6107
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to