Not only mfr's requirements, which at least one mfr. gives you specific length 
within heated space to prevent freezing of water behind/above the dry 
sprinkler, but also now mandated when added to the 2007 edition of 13.  See 
8.4.10.1.  Looked this up recently after seeing freeze-up of fitting in heated 
canopy above sprinkler on a -6 degree night. Just like putting dry pendents 
through the insulated ceiling of a freezer supplied by wet pipe above.  The 
heat in the wet pipe is conducted away through the dry sprinkler.  Insulating 
around the dry sprinkler barrel actually hinders heat getting into the barrel 
and makes it colder at the water interface.

Dave 

David A. de Vries, P.E.
Firetech Engineering Incorporated 




--- On Mon, 2/21/11, Scott A. Futrell <[email protected]> wrote:


From: Scott A. Futrell <[email protected]>
Subject: RE: Dry Sidewalls at back patio
To: [email protected]
Date: Monday, February 21, 2011, 9:02 PM


12" to 18" or more in Minnesota and other northern states to comply with
mfr's requirements.  Don't forget, 10-yr inspection requirement.
Conceal dry type sprinklers above sheetrock in CPVC and it'll be tough
to check them in 10 years without other problems.  Better have some
design conferences with the architect before they go in...

Scott Futrell

(763) 425-1001 Office
(612) 759-5556 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Jamie.seidl
Sent: Monday, February 21, 2011 5:03 PM
To: [email protected]; [email protected]
Subject: Re: Dry Sidewalls at back patio

We've always concealed them in a soffit or perpendicular wall.  As long
as the insulation is at the exterior wall you'll be fine.  Not really
sure where he is coming from with that.  You are still within the heated
envelope of the building.

Jamie
Sent from my iPhone

On Feb 21, 2011, at 5:53 PM, "Travis Mack, SET" <[email protected]>
wrote:

> How is everyone installing these heads when req'd?  One of my
customers just left a meeting with the Tyco Rep and he was told that you
were required to have x" of dry barrel exposed (depending on
temperatures) in the room, and that it could not be concealed in a
soffit or decoshield.  We can't see some of these high end apts or
condos allowing 4-6" of exposed dry barrel in a unit.  What are others
in cold climates doing with these situations?
> 
> -- 
> Please feel free to call if you have any questions or comments.
> 
> Sincerely,
> 
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> Office (480) 505-9271
> Fax (866) 430-6107
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to