If they are located on a fire wall, they must be metallic...
If not I have no idea.

On Fri, Mar 4, 2011 at 3:46 PM, Eric Tysinger <[email protected]> wrote:

> My understanding is that anything beyond semi-recessed is not required to
> be listed. I have talked to a particular manufacturer who confirmed this. If
> you think about it, once you extend the sprinkler beyond this point, your
> are essentially just sealing the hole around the pipe/fitting. In reality
> you are making it look pretty.
>
>
> Thanks,
> Eric Tysinger CET
> NICET III - 108988
> Designer
> Wayne Automatic Fire Sprinklers, Inc.
> 4370 Motorsport Drive
> Concord, NC 28027
> p: (704)782-3032 x1751
> f: (704)795-6838
> C: (239)633-9703
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Matthew J. Willis
> Sent: Friday, March 04, 2011 4:30 PM
> To: [email protected]; [email protected]
> Subject: RE: Plastic Escutcheons
>
> I have decided to quote alum (painted white), with a stainless option.
> To answer your questions Andy, yes the 1/2" are listed. I do not know if
> drilling them voids it. The problem arises in that I have no paper document
> to submit to the state showing approval. The only one available is for the
> 1/2"
>
>
> R/
> Matt
>
>
>
>
> Matthew J. Willis
> Automatic Fire Sprinklers
> Norred Fire Systems L.L.C.
> 318-387-1134 Voice
> 318-816-1087 Mobile
> 318-387-1163 Facsimile
> [email protected]
>
> > >-----Original Message-----
> > >From: [email protected]
> > >[mailto:sprinklerforum- [email protected]] On Behalf Of Andy
> > >Johnston
> > >Sent: Friday, March 04, 2011 3:24 PM
> > >To: Sprinklerforum
> > >Subject: Re: Plastic Escutcheons
> > >
> > >Are the 1/2" listed?
> > >Would drilling them out void there listing?  I've see people use the
> > >two piece snap arounds used but have not found a listed one to meet
> code.
> > >Andy
> > >The information contained in this transmission is privileged and
> > >confidential. No reader may make any use of it's contents with out
> > >the written approval of the sender. The recipient should not act or
> > >use the information in this transmission or any of its attachments
> > >without separate authentication of its authenticity or approval.  If
> > >you have received this in error I apologize please notify me so I can
> > >correct my records. Thank you for your cooperation.
> > >
> > >-----Original Message-----
> > >From: "Morey, Mike" <[email protected]>
> > >Sender: [email protected]
> > >Date: Fri, 4 Mar 2011 14:59:40
> > >To: <[email protected]>
> > >Reply-To: [email protected]
> > >Subject: RE: Plastic Escutcheons
> > >
> > >I think you'd have better luck trying to source a stainless
> > >escutcheon (assuming that's acceptable, which it seems like it should
> > >be?), Vikings "standard flat" is available in 3/4 stainless for
> > >example.  Seems like the listing process would be prohibitive for
> > >such a small market when you can just make them from non ferrous
> > >metal?  Not that being listed has stopped manufacturers from making
> > >escutcheons which should be listed without a listing at all...
> > >
> > >-Mike Morey, SET
> > >Sprinkler Designer
> > >BMW Constructors, Inc.
> > >office: 317-651-0596
> > >mobile: 317-439-2695
> > >
> > >
> > >
> > >-----Original Message-----
> > >From: [email protected] on behalf of Matthew J.
> > >Willis
> > >Sent: Fri 3/4/2011 2:55 PM
> > >To: [email protected]
> > >Subject: RE: Plastic Escutcheons
> > >
> > >Yes you can, if they are listed, and are not for recessed or flush.
> > >Those must be listed with sprinkler as an assembly. This is going to
> > >be food process...
> > >R/
> > >Matt
> > >
> > >
> > >
> > >
> > >
> > >Matthew J. Willis
> > >Automatic Fire Sprinklers
> > >Norred Fire Systems L.L.C.
> > >318-387-1134 Voice
> > >318-816-1087 Mobile
> > >318-387-1163 Facsimile
> > >[email protected]
> > >
> > >> >-----Original Message-----
> > >> >From: [email protected]
> > >> >[mailto:sprinklerforum- [email protected]] On Behalf Of
> > >> >Todd Williams
> > >> >Sent: Friday, March 04, 2011 1:53 PM
> > >> >To: [email protected]; Charles Thurston
> > >> >Subject: Re: Plastic Escutcheons
> > >> >
> > >> >What are you using them for? I don't think you can on sprinklers.
> > >> >
> > >> >
> > >> >At 02:49 PM 3/4/2011, you wrote:
> > >> >>Hello Matthew,
> > >> >>
> > >> >>Have you tried Argo,  Sorry no number handy
> > >> >>
> > >> >>Friday, March 4, 2011, 2:31:53 PM, you wrote:
> > >> >>
> > >> >> > I am having trouble finding ¾" style 401 plastic. Anybody know
> > >> >> > if
> > >> >they are
> > >> >> > available? 2 main suppliers only have ½"
> > >> >>
> > >> >> >
> > >> >>
> > >> >> > Thanks,
> > >> >>
> > >> >> >
> > >> >>
> > >> >> > Matt
> > >> >>
> > >> >> >
> > >> >>
> > >> >> >
> > >> >>
> > >> >> > Matthew J. Willis
> > >> >>
> > >> >> > Automatic Fire Sprinklers
> > >> >>
> > >> >> > Norred Fire Systems L.L.C.
> > >> >>
> > >> >> > 318-387-1134 Voice
> > >> >>
> > >> >> > 318-816-1087 Mobile
> > >> >>
> > >> >> > 318-387-1163 Facsimile
> > >> >>
> > >> >> > [email protected]
> > >> >>
> > >> >> >
> > >> >>
> > >> >> >_______________________________________________
> > >> >> > Sprinklerforum mailing list
> > >> >> > [email protected]
> > >> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerfor
> > >> >> >um
> > >> >>
> > >> >> > For Technical Assistance, send an email to:
> > >[email protected]
> > >> >>
> > >> >> > To Unsubscribe, send an email to:Sprinklerforum-
> > >> >[email protected]
> > >> >> > (Put the word unsubscribe in the subject field)
> > >> >>
> > >> >>
> > >> >>
> > >> >>--
> > >> >>Best regards,
> > >> >>  Charles Thurston
> > >> >mailto:[email protected]
> > >> >>   Coastal Fire Protection/ Myrtle Beach Fire & Safety Group.
> > >> >>    AFAA Guest
> > >> >>
> > >> >>Electronic Privacy Notice:
> > >> >>This e-mail, and any attachments, contains information that is,
> > >> >>or
> > >may
> > >> >>be, covered by electronic communications privacy laws, and is
> > >> >>also confidential and proprietary in nature. If you are not the
> > >> >>intended recipient, please be advised that you are legally
> > >> >>prohibited from retaining, using, copying, distributing, or
> > >> >>otherwise disclosing this information in any manner. Instead,
> > >> >>please reply to the sender that you have received this
> > >> >>communication in error, and then immediately delete it. Thank you
> > >> >>in advance for your cooperation
> > >> >>
> > >> >>_______________________________________________
> > >> >>Sprinklerforum mailing list
> > >> >>[email protected]
> > >> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >> >>
> > >> >>For Technical Assistance, send an email to:
> > >> >>[email protected]
> > >> >>
> > >> >>To Unsubscribe, send an email to:Sprinklerforum-
> > >> >[email protected]
> > >> >>(Put the word unsubscribe in the subject field)
> > >> >
> > >> >Todd G. Williams, PE
> > >> >Fire Protection Design/Consulting
> > >> >Stonington, CT
> > >> >860.535.2080
> > >> >www.fpdc.com
> > >> >
> > >> >_______________________________________________
> > >> >Sprinklerforum mailing list
> > >> >[email protected]
> > >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >> >
> > >> >For Technical Assistance, send an email to:
> > >> >[email protected]
> > >> >
> > >> >To Unsubscribe, send an email to:Sprinklerforum-
> > >[email protected]
> > >> >(Put the word unsubscribe in the subject field) No virus found in
> > >> >this incoming message.
> > >> >Checked by AVG - www.avg.com
> > >> >Version: 9.0.872 / Virus Database: 271.1.1/3466 - Release Date:
> > >03/04/11
> > >> >01:34:00
> > >
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email
> > >to:[email protected]
> > >(Put the word unsubscribe in the subject field)
> > >
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email
> > >to:[email protected]
> > >(Put the word unsubscribe in the subject field)
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email
> > >to:[email protected]
> > >(Put the word unsubscribe in the subject field)
> > >
> > >No virus found in this incoming message.
> > >Checked by AVG - www.avg.com
> > >Version: 9.0.872 / Virus Database: 271.1.1/3466 - Release Date:
> > >03/04/11 01:34:00
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to