Usually it is a Factory Mutual requirement, not NFPA.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, March 07, 2011 10:59 AM
To: [email protected]
Subject: RE: Galvanized Pipe

Nowhere does it say you can't use Galv.  It just doesn't say it's required, 
that's the issue at hand.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Eric Tysinger
Sent: Monday, March 07, 2011 11:01 AM
To: [email protected]
Subject: RE: Galvanized Pipe

Also look at NFPA 13, 2002. 
Table 14.4.4.5.

They wouldn't give you c-values for black dry pipe and pre-action systems if 
you couldn't use it. 


Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Monday, March 07, 2011 10:56 AM
To: [email protected]
Subject: RE: Galvanized Pipe

8.4.7 (and everything within 8.4.7) is LARGE DROP SPRINKLERS

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Monday, March 07, 2011 9:49 AM
To: [email protected]
Subject: Galvanized Pipe

 

8.4.7.2.1. (2007) Calls for steel pipe used in Dry Pipe and Pre-action systems 
to be internally galvanized, the handbook adds additional information saying 
this only applies to systems with Large Drop sprinklers.
How can I use this "added text" to explain to an AHJ that says NFPA requires 
galvanized pipe for any type of a dry system?



Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476







=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950) 
http://www.pctools.com/ ======= _______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1204 / Virus Database: 1435/3487 - Release Date: 03/07/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely for the 
intended recipient(s). If you are not the named recipient you should not read, 
distribute, copy or alter this email. Any views or opinions expressed in this 
email are those of the author and do not represent those of the  company. 
Warning: Although precautions have been taken to make sure no viruses are 
present in this email, the company cannot accept responsibility for any loss or 
damage that arise from the use of this email or attachments.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to