Brian just remember 8.4.7.2 is not the only place galvanized pipe is
required in 13. There are systems and portions of systems that require galv.
Pipe, that are not large drop systems. Such as 8.3.4.3.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Monday, March 07, 2011 9:03 AM
To: [email protected]
Subject: RE: Galvanized Pipe

I'm such a turd, all I can say is it's Monday! Thanks guys......

Brian Harris
FDFP Inc.
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Monday, March 07, 2011 10:56 AM
To: [email protected]
Subject: RE: Galvanized Pipe

8.4.7 (and everything within 8.4.7) is LARGE DROP SPRINKLERS

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Monday, March 07, 2011 9:49 AM
To: [email protected]
Subject: Galvanized Pipe

 

8.4.7.2.1. (2007) Calls for steel pipe used in Dry Pipe and Pre-action
systems to be internally galvanized, the handbook adds additional
information saying this only applies to systems with Large Drop sprinklers.
How can I use this "added text" to explain to an AHJ that says NFPA requires
galvanized pipe for any type of a dry system?



Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476







=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1204 / Virus Database: 1435/3487 - Release Date: 03/07/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to