Because section 8.4.7 replies to large drop sprinklers only. Thus, 8.4.7.2 is a subsection to the large drop requirements only.
Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: Brian Harris [mailto:[email protected]] Sent: Monday, March 07, 2011 10:49 AM To: [email protected] Subject: Galvanized Pipe 8.4.7.2.1. (2007) Calls for steel pipe used in Dry Pipe and Pre-action systems to be internally galvanized, the handbook adds additional information saying this only applies to systems with Large Drop sprinklers. How can I use this "added text" to explain to an AHJ that says NFPA requires galvanized pipe for any type of a dry system? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)