Because section 8.4.7 replies to large drop sprinklers only.  Thus, 8.4.7.2 is 
a subsection to the large drop requirements only.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Brian Harris [mailto:[email protected]] 
Sent: Monday, March 07, 2011 10:49 AM
To: [email protected]
Subject: Galvanized Pipe

8.4.7.2.1. (2007) Calls for steel pipe used in Dry Pipe and Pre-action
systems to be internally galvanized, the handbook adds additional
information saying this only applies to systems with Large Drop sprinklers.
How can I use this "added text" to explain to an AHJ that says NFPA requires
galvanized pipe for any type of a dry system?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16950)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to