Nice Bad Moodsville. Hackles up and full of bile. Matthew you might
also take a piece of furniture and a box of something to store and ask
him to demonstrate how he can habitate or store something above an
ACT. He f***** up and is trying to save his a** at your expense.

On Tue, Mar 8, 2011 at 4:44 PM, steve <[email protected]> wrote:
> He is completely, totally full of crap.  Or sadly, badly mistaken, if you 
> give him the benefit of the doubt.  Ask him to submit to the AHJ for an 
> interp, or bring in a consultant to explain accessibility.  That's a code 
> defined concept and if it's "accessible" then ADA applies in a school, no?   
> Ask hime for his egress plan for the affected spaces.
>
> Idiots.
>
> SML
> Bad Moodsville
>
>
> Sent from my Verizon Wireless BlackBerry
>
> -----Original Message-----
> From: "Martin, Matthew" <[email protected]>
> Sender: [email protected]
> Date: Tue, 8 Mar 2011 19:25:15
> To: [email protected]<[email protected]>
> Reply-To: [email protected]
> Subject: RE: Interstitial Space
>
> Thank you all for your input. It has helped me confirm that my argument is on 
> the right track. We are arguing about $190,000. They want to pull from a 
> change that is about 80% complete.
>  I have received a new rebuttal from the architect it is;
>
>        Per NFPA 13 8.14.1.2.2  (2002) "noncombustible and limited combustible 
> concealed spaces with limited access and not permitting occupancy or storage 
> of combustibles shall not require sprinkler protection.  The space shall be 
> considered a concealed space even with small openings such as those used as 
> return air for a plenum", sprinkling of interstitial space above ACT (i.e. 
> classrooms) is required.  ACT is not considered limited access to the 
> concealed space.  All portion of an ACT ceiling is accessible
>
> Is his contention that acoustical tile ceiling is accessible.
>  My argument will be that no one will be occupying that space and nothing 
> will be stored in that space. The only reason anyone will be up there is for 
> servicing something. An ACT suspended ceiling fits into this code section.
> Thanks,
>
> Matt
>
>
>
>
> Matthew Martin
> CQC Manager
> Suffolk Construction Company, Inc.
> Direct: 323-781-1778
> Cell: 949-892-7419
>
> www.suffolkconstruction.com
>
> Please consider the environment before printing this e-mail-----Original 
> Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Steve Leyton
> Sent: Monday, March 07, 2011 3:17 PM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> 2001 CBC allows a 4-story building if Type II- FR.   It allows only two
> stories if Type II-One Hour.   If you're sure that the buildings are
> II-FR and if return air is ducted, then it sounds like a construction
> documents conflict and I would agree with you that sprinklers may not be
> required by code.
>
> Steve
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Martin,
> Matthew
> Sent: Monday, March 07, 2011 2:37 PM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> I should amend my last remarks;
>  The three buildings that are using sprinklers as a fire resistive
> substitution WE ARE installing sprinklers in the interstitial space. It
> is the four story Type II-FR buildings where we are arguing with the
> design team. There is no note on the plans to use fire sprinklers a
> substitution at those buildings. So the "note" is listed on three
> buildings and note listed on three other buildings.
>
>
>
> Matthew Martin
> CQC Manager
> Suffolk Construction Company, Inc.
> Direct: 323-781-1778
> Cell: 949-892-7419
>
> www.suffolkconstruction.com
>
> Please consider the environment before printing this e-mail-----Original
> Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Gregg
> Fontes
> Sent: Monday, March 07, 2011 1:23 PM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> We have done many DSA projects in our neck of California, if sprinklers
> are
> used for substitutions, above ceilings are sprinkled.  No and, if, or
> buts.
>
> Thanks,
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> 209-334-9119
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Monday, March 07, 2011 1:18 PM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> Sorry dude, see CSFM 03-30:
> http://osfm.fire.ca.gov/codeinterpretation/pdf/2003/03_030.pdf
>
> Pursuant to a question regarding the use of sprinklers in
> non-combustible interstitial space to satisfy Sect. 508 of 2001 CBC, the
> answer is: "When an automatic sprinkler system is used for fire
> resistive substitution, complete sprinkler coverage is required.
> Sprinkler omissions allowed by NFPA 13 are not permitted in this case."
>
> Steve
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Martin,
> Matthew
> Sent: Monday, March 07, 2011 1:12 PM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> We are on the 2001 CBC. Type II FR can be as high as 4 stories.
> We have six buildings on this project. three of the buildings noted on
> the Building Code Data Table that sprinklers are used for fire resistive
> substitution.
> The interstitial space above the classrooms is used only for relief air.
> The return air is connected to the duct system.
>  I am relying on IR9-1 2.3 for backing up the my argument against the
> "requirement" of uprights in the areas not noted as using sprinklers in
> lieu of fire resistive construction. All the space above the ceilings is
> non-combustible and the construction between floors is 2 hour
> construction.
> The following is from the table for the specific Building I am dealing
> with.
>
> BUILDING 2 SMALL LEARNING CENTERS
> FIRE SPRINKLERS
> FULLY SPRINKLERED
>
> FIRE RESISTIVE REQUIREMENTS
> (CBC TABLE 6-A)
> BEARING WALLS - EXTERIOR                        4 - SEC. 603.3.1
> BEARING WALLS - INTERIOR                        2
> NONBEARING WALLS - EXTERIOR             4 - SEC. 603.3.1
> STRUCTURAL FRAME                                2
> PARTITIONS - PERMANENT                  1
> SHAFT ENCLOSURES                                2
> FLOORS AND FLOOR-CEILING                        2
> ROOFS AND ROOF-CEILINGS                         1 - SEC. 603.5
> EXTERIOR DOORS AND WINDOWS              SEC 603.3.2
>
>
>
>
> Matthew Martin
> CQC Manager
> Suffolk Construction Company, Inc.
> Direct: 323-781-1778
> Cell: 949-892-7419
>
> www.suffolkconstruction.com
>
> Please consider the environment before printing this e-mail-----Original
> Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Monday, March 07, 2011 12:39 PM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> I've been in meeting that prevented me from chiming in earlier.   You
> have opened one of the great buckets of worms that DSA has in their
> closet, but I should caution you that there are a couple of California
> interps and code requirements that absolutely may compel the
> installation of sprinklers in non-combustible attics and interstitial
> spaces.
>
> I'm assuming that this is a deferred submittal, yes?   And as such
> you're working under 2007 CBC?   If so, my first question is, are
> sprinklers being used by the architect in lieu of fire-rated
> construction?  A Type II building can only be 2-stories if it's II-B, so
> in order to make it II-A they will have to spray the structure with
> Monokote or use the sprinklers.  And that's to get three floors - to get
> the fourth they have to count the sprinklers.  And for E-occupancy, you
> can't take both an area increase in addition to the height increase
> (CSFM amendment) without some alternative means and methods.   CSFM
> Formal Interpretation 03-30 states that where sprinklers are used in
> lieu of fire resistive construction, all areas of the building -
> including interstitial and concealed spaces - shall be sprinklered
> regardless of combustibility of structure.
>
> I would also call your attention to 907.2.3.6.1 which is the requirement
> for smoke detection in "ceiling-plenums" where interstitial spaces are
> used for return air.   In an e-occupancy, such spaces require smoke
> detection or sprinklers in the plenum spaces, regardless of
> combustibility.   Did you review the architect's code analysis?   Do
> they note that sprinklers are being taken in lieu of fire-resistive
> construction and/or detection in plenum spaces?
>
> Steve Leyton
> Sick To My Stomach That I Can Recite All of That From Memory
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Martin,
> Matthew
> Sent: Monday, March 07, 2011 11:50 AM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> The heat detectors were specifically excluded from the drawings
>
>
>
> Matthew Martin
> CQC Manager
> Suffolk Construction Company, Inc.
> Direct: 323-781-1778
> Cell: 949-892-7419
>
> www.suffolkconstruction.com
>
> Please consider the environment before printing this e-mail-----Original
> Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George
> Church
> Sent: Monday, March 07, 2011 11:48 AM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> If you end up with "HERE'S THE EXTRA YOU OWE US" then yes, you're on the
> right track.
> Might be you owe em a credit from the FA guy for the detectors not
> installed, but I'll bet the SSU were a lot more.
>
> Taking their everywhere and completely would have you providing
> sprinklers 16" on center above all the wall cavities formed by vertical
> metal studs, inside all the ductwork, and in California- I can't even
> render a guess as to what other cavities might require protection.
>
> George Church
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Martin,
> Matthew
> Sent: Monday, March 07, 2011 2:41 PM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> Thank you for all the answers so far.  Here is some further
> clarifications.
>  Our project is a new high school in Los Angeles , CA.
>  The buildings in question are 4 story classroom buildings with the
> space between floors of about 36"-40" of non combustible space.
> The argument we are having is that the upright sprinklers are not
> required based on NFPA 8.14.1.2 (2002). Many of you have confirmed our
> argument, thank you. The design team directed us to install them about
> eight months ago and planned on paying us for the work. Now they are
> saying they were required because fully means "everywhere and
> completely." Part of my argument back will be that they wanted the
> upright sprinklers installed in lieu of heat detectors. It is heat
> detectors that are required for activation of the fire alarm system. The
> sprinkler system ( uprights) here is not being used as a suppression
> system but as an activation system. Am I on the right track?
>
>
>
> Matthew Martin
> CQC Manager
> Suffolk Construction Company, Inc.
> Direct: 323-781-1778
> Cell: 949-892-7419
>
> www.suffolkconstruction.com
>
> Please consider the environment before printing this e-mail-----Original
> Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George
> Church
> Sent: Monday, March 07, 2011 11:23 AM
> To: [email protected]
> Subject: RE: Interstitial Space
>
> Clearly there's a HUGE dif between an interstitial space above a drop
> ceiling and below the deck above, and the vision you made me remember of
> an animal research lab at Merck with 15' high interstitial spaces with
> grated floors throughout. In that one, sprinklers were installed in the
> noncombustible concealed space because with the doorways accessing the
> grated platform, it was no longer concealed.
>
> Another point to consider when dealing with pharmaceuticals, clean
> rooms, bio and nanotechnologies, is the dollar values involved (or
> business interruption) may cause an Owner or insurance carrier to ask
> for sprinkler protection beyond that required by minimum consensus
> standards.
>
> George Church
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Monday, March 07, 2011 2:11 PM
> To: [email protected]
> Subject: Re: Interstitial Space
>
> For many industrial projects, especial biotech and microelectronics,
> interstitial space is commonly used to describe the space between floors
> - especially where the spaces are tall enough to accommodate personnel.
>
> I am now gun shy enough to where I plan full automatic sprinkler
> protection throughout interstitial spaces.  We once got burned where the
> local AHJ's signed off in writing that the interstitial spaces did not
> have to be sprinklered only to be told a year later that they would
> require protection based on a new evaluation by a code consultant.  We
> had been told that minimal plastic drain pipe and fire resistant cable
> was acceptable.
>
> If the interstitial "floor" is a walkable ceiling, you will more than
> likely lose the battle even if the space is non-combustible and has
> non-combustible contents because the argument will be that storage would
> be possible.
>
> Regards,
>
> Jim
>
>
> James L (Jim) Roberts, PE/SET |FLUOR|Central Operations|
> [email protected]|IODC 20.5149 |864.281.5149| www.fluor.com
>
>
>
> From:       Todd Williams <[email protected]>
> To:         [email protected]
> Date:       03/07/2011 01:49 PM
> Subject:    Re: Interstitial Space
> Sent by:    [email protected]
>
>
>
> Interstitial and concealed can be assumed synonymous in our situation.
> Interstitial tends to apply more to things like spaces between walls.
>
>
> At 01:46 PM 3/7/2011, you wrote:
>>Is the space combustible?
>>On Mar 7, 2011 12:39 PM, "Martin, Matthew"
> <[email protected]>
>>wrote:
>> > Can anyone tell me what the NFPA says about the requirements of
> sprinklers
>>in the interstitial space. What is the definition of " Interstitial
> Space"?
>> > Also where in the NFPA is the term Interstitial Space used.
>> > We have an Architect who says that a fully sprinklered building
> includes
>>sprinklers in all the interstitial spaces.
>> >
>> > Thanks in advance,
>> >
>> >
>> >
>> > Matthew Martin
>> > CQC Manager
>> > Suffolk Construction Company, Inc.
>> > Direct: 323-781-1778
>> > Cell: 949-892-7419
>> >
>> > www.suffolkconstruction.com
>> >
>> > Please consider the environment before printing this e-mail
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > For Technical Assistance, send an email to:
>> > [email protected]
>> >
>> > To Unsubscribe, send an email
> to:[email protected]
>> > (Put the word unsubscribe in the subject field)
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> ------------------------------------------------------------
> The information transmitted is intended only for the person or entity to
> which it is addressed and may contain proprietary, business-confidential
> and/or privileged material.
> If you are not the intended recipient of this message you are hereby
> notified that any use, review, retransmission, dissemination,
> distribution, reproduction or any action taken in reliance upon this
> message is prohibited. If you received this in error, please contact the
> sender and delete the material from any computer.
>
> Any views expressed in this message are those of the individual sender
> and may not necessarily reflect the views of the company.
> ------------------------------------------------------------
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to