Thank you all for your input. It has helped me confirm that my argument is on 
the right track. We are arguing about $190,000. They want to pull from a change 
that is about 80% complete.
 I have received a new rebuttal from the architect it is;

        Per NFPA 13 8.14.1.2.2  (2002) "noncombustible and limited combustible 
concealed spaces with limited access and not permitting occupancy or storage of 
combustibles shall not require sprinkler protection.  The space shall be 
considered a concealed space even with small openings such as those used as 
return air for a plenum", sprinkling of interstitial space above ACT (i.e. 
classrooms) is required.  ACT is not considered limited access to the concealed 
space.  All portion of an ACT ceiling is accessible

Is his contention that acoustical tile ceiling is accessible.
 My argument will be that no one will be occupying that space and nothing will 
be stored in that space. The only reason anyone will be up there is for 
servicing something. An ACT suspended ceiling fits into this code section.
Thanks,

Matt




Matthew Martin
CQC Manager
Suffolk Construction Company, Inc.
Direct: 323-781-1778
Cell: 949-892-7419

www.suffolkconstruction.com

Please consider the environment before printing this e-mail-----Original 
Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Monday, March 07, 2011 3:17 PM
To: [email protected]
Subject: RE: Interstitial Space

2001 CBC allows a 4-story building if Type II- FR.   It allows only two
stories if Type II-One Hour.   If you're sure that the buildings are
II-FR and if return air is ducted, then it sounds like a construction
documents conflict and I would agree with you that sprinklers may not be
required by code.

Steve



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Martin,
Matthew
Sent: Monday, March 07, 2011 2:37 PM
To: [email protected]
Subject: RE: Interstitial Space

I should amend my last remarks;
 The three buildings that are using sprinklers as a fire resistive
substitution WE ARE installing sprinklers in the interstitial space. It
is the four story Type II-FR buildings where we are arguing with the
design team. There is no note on the plans to use fire sprinklers a
substitution at those buildings. So the "note" is listed on three
buildings and note listed on three other buildings.



Matthew Martin
CQC Manager
Suffolk Construction Company, Inc.
Direct: 323-781-1778
Cell: 949-892-7419

www.suffolkconstruction.com

Please consider the environment before printing this e-mail-----Original
Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Gregg
Fontes
Sent: Monday, March 07, 2011 1:23 PM
To: [email protected]
Subject: RE: Interstitial Space

We have done many DSA projects in our neck of California, if sprinklers
are
used for substitutions, above ceilings are sprinkled.  No and, if, or
buts.

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Monday, March 07, 2011 1:18 PM
To: [email protected]
Subject: RE: Interstitial Space

Sorry dude, see CSFM 03-30:
http://osfm.fire.ca.gov/codeinterpretation/pdf/2003/03_030.pdf

Pursuant to a question regarding the use of sprinklers in
non-combustible interstitial space to satisfy Sect. 508 of 2001 CBC, the
answer is: "When an automatic sprinkler system is used for fire
resistive substitution, complete sprinkler coverage is required.
Sprinkler omissions allowed by NFPA 13 are not permitted in this case."

Steve


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Martin,
Matthew
Sent: Monday, March 07, 2011 1:12 PM
To: [email protected]
Subject: RE: Interstitial Space

We are on the 2001 CBC. Type II FR can be as high as 4 stories.
We have six buildings on this project. three of the buildings noted on
the Building Code Data Table that sprinklers are used for fire resistive
substitution.
The interstitial space above the classrooms is used only for relief air.
The return air is connected to the duct system.
 I am relying on IR9-1 2.3 for backing up the my argument against the
"requirement" of uprights in the areas not noted as using sprinklers in
lieu of fire resistive construction. All the space above the ceilings is
non-combustible and the construction between floors is 2 hour
construction.
The following is from the table for the specific Building I am dealing
with.

BUILDING 2 SMALL LEARNING CENTERS
FIRE SPRINKLERS
FULLY SPRINKLERED

FIRE RESISTIVE REQUIREMENTS
(CBC TABLE 6-A)
BEARING WALLS - EXTERIOR                        4 - SEC. 603.3.1
BEARING WALLS - INTERIOR                        2
NONBEARING WALLS - EXTERIOR             4 - SEC. 603.3.1
STRUCTURAL FRAME                                2
PARTITIONS - PERMANENT                  1
SHAFT ENCLOSURES                                2
FLOORS AND FLOOR-CEILING                        2
ROOFS AND ROOF-CEILINGS                         1 - SEC. 603.5
EXTERIOR DOORS AND WINDOWS              SEC 603.3.2




Matthew Martin
CQC Manager
Suffolk Construction Company, Inc.
Direct: 323-781-1778
Cell: 949-892-7419

www.suffolkconstruction.com

Please consider the environment before printing this e-mail-----Original
Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Monday, March 07, 2011 12:39 PM
To: [email protected]
Subject: RE: Interstitial Space

I've been in meeting that prevented me from chiming in earlier.   You
have opened one of the great buckets of worms that DSA has in their
closet, but I should caution you that there are a couple of California
interps and code requirements that absolutely may compel the
installation of sprinklers in non-combustible attics and interstitial
spaces.

I'm assuming that this is a deferred submittal, yes?   And as such
you're working under 2007 CBC?   If so, my first question is, are
sprinklers being used by the architect in lieu of fire-rated
construction?  A Type II building can only be 2-stories if it's II-B, so
in order to make it II-A they will have to spray the structure with
Monokote or use the sprinklers.  And that's to get three floors - to get
the fourth they have to count the sprinklers.  And for E-occupancy, you
can't take both an area increase in addition to the height increase
(CSFM amendment) without some alternative means and methods.   CSFM
Formal Interpretation 03-30 states that where sprinklers are used in
lieu of fire resistive construction, all areas of the building -
including interstitial and concealed spaces - shall be sprinklered
regardless of combustibility of structure.

I would also call your attention to 907.2.3.6.1 which is the requirement
for smoke detection in "ceiling-plenums" where interstitial spaces are
used for return air.   In an e-occupancy, such spaces require smoke
detection or sprinklers in the plenum spaces, regardless of
combustibility.   Did you review the architect's code analysis?   Do
they note that sprinklers are being taken in lieu of fire-resistive
construction and/or detection in plenum spaces?

Steve Leyton
Sick To My Stomach That I Can Recite All of That From Memory




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Martin,
Matthew
Sent: Monday, March 07, 2011 11:50 AM
To: [email protected]
Subject: RE: Interstitial Space

The heat detectors were specifically excluded from the drawings



Matthew Martin
CQC Manager
Suffolk Construction Company, Inc.
Direct: 323-781-1778
Cell: 949-892-7419

www.suffolkconstruction.com

Please consider the environment before printing this e-mail-----Original
Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Monday, March 07, 2011 11:48 AM
To: [email protected]
Subject: RE: Interstitial Space

If you end up with "HERE'S THE EXTRA YOU OWE US" then yes, you're on the
right track.
Might be you owe em a credit from the FA guy for the detectors not
installed, but I'll bet the SSU were a lot more.

Taking their everywhere and completely would have you providing
sprinklers 16" on center above all the wall cavities formed by vertical
metal studs, inside all the ductwork, and in California- I can't even
render a guess as to what other cavities might require protection.

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Martin,
Matthew
Sent: Monday, March 07, 2011 2:41 PM
To: [email protected]
Subject: RE: Interstitial Space

Thank you for all the answers so far.  Here is some further
clarifications.
 Our project is a new high school in Los Angeles , CA.
 The buildings in question are 4 story classroom buildings with the
space between floors of about 36"-40" of non combustible space.
The argument we are having is that the upright sprinklers are not
required based on NFPA 8.14.1.2 (2002). Many of you have confirmed our
argument, thank you. The design team directed us to install them about
eight months ago and planned on paying us for the work. Now they are
saying they were required because fully means "everywhere and
completely." Part of my argument back will be that they wanted the
upright sprinklers installed in lieu of heat detectors. It is heat
detectors that are required for activation of the fire alarm system. The
sprinkler system ( uprights) here is not being used as a suppression
system but as an activation system. Am I on the right track?



Matthew Martin
CQC Manager
Suffolk Construction Company, Inc.
Direct: 323-781-1778
Cell: 949-892-7419

www.suffolkconstruction.com

Please consider the environment before printing this e-mail-----Original
Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Monday, March 07, 2011 11:23 AM
To: [email protected]
Subject: RE: Interstitial Space

Clearly there's a HUGE dif between an interstitial space above a drop
ceiling and below the deck above, and the vision you made me remember of
an animal research lab at Merck with 15' high interstitial spaces with
grated floors throughout. In that one, sprinklers were installed in the
noncombustible concealed space because with the doorways accessing the
grated platform, it was no longer concealed.

Another point to consider when dealing with pharmaceuticals, clean
rooms, bio and nanotechnologies, is the dollar values involved (or
business interruption) may cause an Owner or insurance carrier to ask
for sprinkler protection beyond that required by minimum consensus
standards.

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, March 07, 2011 2:11 PM
To: [email protected]
Subject: Re: Interstitial Space

For many industrial projects, especial biotech and microelectronics,
interstitial space is commonly used to describe the space between floors
- especially where the spaces are tall enough to accommodate personnel.

I am now gun shy enough to where I plan full automatic sprinkler
protection throughout interstitial spaces.  We once got burned where the
local AHJ's signed off in writing that the interstitial spaces did not
have to be sprinklered only to be told a year later that they would
require protection based on a new evaluation by a code consultant.  We
had been told that minimal plastic drain pipe and fire resistant cable
was acceptable.

If the interstitial "floor" is a walkable ceiling, you will more than
likely lose the battle even if the space is non-combustible and has
non-combustible contents because the argument will be that storage would
be possible.

Regards,

Jim


James L (Jim) Roberts, PE/SET |FLUOR|Central Operations|
[email protected]|IODC 20.5149 |864.281.5149| www.fluor.com



From:       Todd Williams <[email protected]>
To:         [email protected]
Date:       03/07/2011 01:49 PM
Subject:    Re: Interstitial Space
Sent by:    [email protected]



Interstitial and concealed can be assumed synonymous in our situation.
Interstitial tends to apply more to things like spaces between walls.


At 01:46 PM 3/7/2011, you wrote:
>Is the space combustible?
>On Mar 7, 2011 12:39 PM, "Martin, Matthew"
<[email protected]>
>wrote:
> > Can anyone tell me what the NFPA says about the requirements of
sprinklers
>in the interstitial space. What is the definition of " Interstitial
Space"?
> > Also where in the NFPA is the term Interstitial Space used.
> > We have an Architect who says that a fully sprinklered building
includes
>sprinklers in all the interstitial spaces.
> >
> > Thanks in advance,
> >
> >
> >
> > Matthew Martin
> > CQC Manager
> > Suffolk Construction Company, Inc.
> > Direct: 323-781-1778
> > Cell: 949-892-7419
> >
> > www.suffolkconstruction.com
> >
> > Please consider the environment before printing this e-mail
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to:
> > [email protected]
> >
> > To Unsubscribe, send an email
to:[email protected]
> > (Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


------------------------------------------------------------
The information transmitted is intended only for the person or entity to
which it is addressed and may contain proprietary, business-confidential
and/or privileged material.
If you are not the intended recipient of this message you are hereby
notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon this
message is prohibited. If you received this in error, please contact the
sender and delete the material from any computer.

Any views expressed in this message are those of the individual sender
and may not necessarily reflect the views of the company.
------------------------------------------------------------

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to