For the designer: 46 sub-points under one of the top 5 items: NFPA 13 2010, 22.1.3: Working plans shall...show those items...that pertain to the design of the system.
Bobby McCullough [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Johnson, Duane (NIH/OD/ORS) [C] Sent: Thursday, March 10, 2011 7:07 AM To: [email protected] Subject: top five list I will be a guest lecturer at the Univ of Md next week. I will be providing a list of must do's while preparing sprinkler drawings. Knowing that many students will be going to work for consulting firms and others to installation firms, I want to provide input from both perspectives. So I ask the forum the following questions... here is your chance to provide input to future industry personnel: If you were asked to provide a top 5 list that an engineer should do/identify on a sprinkler design, what would they be? What are the first 5 items a sprinkler designer should do when preparing drawings? Feel free to email me direct. Thanks. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)