Along with what Greg says, if we could ever get this actually done correctly
it would make everyone's life much easier when it comes to bidding a job.
How many times have you rolled out a set of plans that were done by a PE or
FPE only to find a combustible attic with no indication anywhere in the
specs or drawings that you need to put sprinklers up there?  If you put them
in your bid, you miss the job.  If you leave them out like most folks do,
you have to eat them because, unlike your competitors, you are supposed to
know that it was wrong and do it anyway!

Cliff Whitfield, SET
President
Fire Design, Inc.
 
[email protected]
www.fire-design.com
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, March 10, 2011 8:23 AM
To: [email protected]; [email protected]
Subject: Re: top five list

1) If they don't KNOW what they are talking about, don't put it on the
drawing - so CONFIRM their information (don't lay out sprinklers and put
branchlines on the drawings as a guess)
2) CONFIRM the Occupancy type and pertinent codes - CRITICAL
3) SPECIFY with thought the design criteria - don't say .10/1,500  if you
will allow reductions and large room rule calcs etc.
4) UNDERSTAND the project
5) WATER SUPPLY ANALYSIS - don't put fire pumps on drawings just to cover
yourself.

The details are easy for contractors to work through. The hard part is
working behind BAD general info, incorrect code references, bad water supply
data, heads laid out that are not even close and a contract that says you
will comply with the (incorrect) drawings, etc.

Greg

On Thu, Mar 10, 2011 at 7:48 AM, Chris Cahill
<[email protected]>wrote:

> I'd combine Craig's 4 and 5 and add a new 5 water supply analysis.
>  Otherwise that is what the A/E should focus on.
>
> Chris
> -----Original Message-----
> From: <[email protected]>
> Sender: [email protected]
> Date: Thu, 10 Mar 2011 06:37:18
> To: <[email protected]>
> Reply-To: [email protected]
> Subject: RE: top five list
>
> Duane,
>
> When you say consulting are you talking about A/E firms?
>
> In real basic, simple terms (definitely not all inclusive):
>
> A/E Fire Protection Specialist:
> 1. Obtain description of the use of the occupancy.
> 2. Identify applicable codes.
> 3. Identify Insurance Underwriter, Risk Consultant, AHJ and any specific
> additional requirements.
> 4. Perform fire hazards analysis.
> 5. Determine fire protection systems design criteria based on hazards
> analysis, applicable codes and any additional requirements.
>
>
> Contractor:  (not design/build)
> 1. Obtain A/E drawings or occupancy descriptions
> 2. Verify water data, code data, system design criteria
> 3. Throw A/E drawings in the trash*
> 4. See list of items under heading of A/E above.
> 5. Prepare installation drawings.
>
>
> *This is not applicable for all A/E submitted drawings and should not be
> taken as an indictment against any A/E firm its engineers, designers or
> other related staff, their families or pets, living or dead or in a
> semi-comatose state stuck at their desk. Your results may vary.
>
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Johnson, Duane
> (NIH/OD/ORS) [C]
> Sent: Thursday, March 10, 2011 7:07 AM
> To: [email protected]
> Subject: top five list
>
> I will be a guest lecturer at the Univ of Md next week.  I will be
> providing a list of must do's while preparing sprinkler drawings.  Knowing
> that many students will be going to work for consulting firms and others
to
> installation firms, I want to provide input from both perspectives.  So I
> ask the forum the following questions... here is your chance to provide
> input to future industry personnel:
>
>
> If you were asked to provide a top 5 list that an engineer should
> do/identify on a sprinkler design, what would they be?
>
>
> What are the first 5 items a sprinkler designer should do when preparing
> drawings?
>
>
> Feel free to email me direct.
> Thanks.
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Support Contractor)
> Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to