Okay, just got off the phone w/ Tyco support and thought I would post here. The keywords are "ceiling construction" in Tyco's listing #2 - ceiling construction pertaining to features of a ceiling itself and not the trusses above a ceiling. Trusses are only mentioned in UL listing #3 with strict criteria such as noncombustible web members. They pointed out to me the previous provision that it needs to be per Nfpa 13 and we went over each point of 8.4.3. and open web trusses (consisting of 2x construction) fails to meet 8.4.3. (1) for "smooth" ceilings / roof and also 8.4.3. (3) web members no greater than 1".
Hope that clarifies for anyone else who's come across this. --- On Mon, 3/14/11, Matt Grise <[email protected]> wrote: From: Matt Grise <[email protected]> Subject: RE: EC Upright in Attic Space To: "'[email protected]'" <[email protected]> Date: Monday, March 14, 2011, 9:17 PM 2007 8.4.3 (2) Unobstructed or noncombustible obstructed where specifically listed for such use. If they do not meet the spacing requirements, then they are improperly applied, but they could be there from a code standpoint. Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ralphy Henderson Sent: Monday, March 14, 2011 4:11 PM To: [email protected] Subject: RE: EC Upright in Attic Space I still don't see anything which would override 8.4.3's reqmnt for smooth, flat ceilings / roof (smooth being defined as 7'-6" + on center) If it could be done I still wouldnt' be able to comply with Tyco's 4x rule; that would mean I need to be 16" away from 2x4 web members that are spaced 24" o/c. I couldn't space it 4x without being too close to one side of the truss or the other.... --- On Mon, 3/14/11, Matt Grise <[email protected]> wrote: From: Matt Grise <[email protected]> Subject: RE: EC Upright in Attic Space To: "'[email protected]'" <[email protected]> Date: Monday, March 14, 2011, 8:56 PM I think it says that if you have members greater than 1", you must apply the 4times rule. I was looking at pg 4 of the cutsheet. Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ralphy Henderson Sent: Monday, March 14, 2011 3:52 PM To: [email protected] Subject: RE: EC Upright in Attic Space 3'-10" I'll have another look at the spec sheet. I thought the Tyco's were only for trusses with a web no greater than 1" (ie. bar joists). Thx, --- On Mon, 3/14/11, Matt Grise <[email protected]> wrote: From: Matt Grise <[email protected]> Subject: RE: EC Upright in Attic Space To: "'[email protected]'" <[email protected]> Date: Monday, March 14, 2011, 8:43 PM What is the distance from the deck to the drop ceiling? The EC 11 heads are listed for unobstructed, combustible construction. Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ralphy Henderson Sent: Monday, March 14, 2011 3:11 PM To: [email protected] Subject: RE: EC Upright in Attic Space Yeah, but I'm looking at an 11.2K e/c at 18x18 in wood trusses. --- On Mon, 3/14/11, Richard Carr <[email protected]> wrote: From: Richard Carr <[email protected]> Subject: RE: EC Upright in Attic Space To: [email protected] Date: Monday, March 14, 2011, 7:52 PM THE Tyco CC2 head will let you do 144 sq. ft. Richard Carr, SET Design Manager Associated Sprinkler Co., LLC 336.373.3901 ext 217 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ralphy Henderson Sent: Monday, March 14, 2011 3:37 PM To: [email protected] Subject: EC Upright in Attic Space I'm looking at some pre-designed fire sprinkler drawings showing extended coverage uprights in a concealed combustible space above a grid ceiling consisting of open web wood trusses (relatively no pitch) at 24" o/c. Looking at 8.4.3. (2007 ed) I don't think this is permissible mainly because of the "smooth, flat" criteria. Am I right? And does someone make an EC upright that can possibly be used in this scenario (besides the Tyco attic sprinklers). Thanks, Ralph _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) This email and any attached files are confidential and intended solely for the intended recipient(s). If you are not the named recipient you should not read, distribute, copy or alter this email. Any views or opinions expressed in this email are those of the author and do not represent those of the company. Warning: Although precautions have been taken to make sure no viruses are present in this email, the company cannot accept responsibility for any loss or damage that arise from the use of this email or attachments. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)