2007 8.4.3 (2) Unobstructed or noncombustible obstructed where specifically 
listed for such use. If they do not meet the spacing requirements, then they 
are improperly applied, but they could be there from a code standpoint.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Monday, March 14, 2011 4:11 PM
To: [email protected]
Subject: RE: EC Upright in Attic Space

I still don't see anything which would override 8.4.3's reqmnt for smooth, flat 
ceilings / roof (smooth being defined as 7'-6" + on center) If it could be done 
I still wouldnt' be able to comply with Tyco's 4x rule; that would mean I need 
to be 16" away from 2x4 web members that are spaced 24" o/c. I couldn't space 
it 4x without being too close to one side of the truss or the other....



--- On Mon, 3/14/11, Matt Grise <[email protected]> wrote:

From: Matt Grise <[email protected]>
Subject: RE: EC Upright in Attic Space
To: "'[email protected]'" <[email protected]>
Date: Monday, March 14, 2011, 8:56 PM

I think it says that if you have members greater than 1", you must apply the 
4times rule. I was looking at pg 4 of the cutsheet.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Monday, March 14, 2011 3:52 PM
To: [email protected]
Subject: RE: EC Upright in Attic Space

3'-10" 

I'll have another look at the spec sheet. I thought the Tyco's were only for 
trusses with a web no greater than 1" (ie. bar joists).

Thx,


--- On Mon, 3/14/11, Matt Grise <[email protected]> wrote:

From: Matt Grise <[email protected]>
Subject: RE: EC Upright in Attic Space
To: "'[email protected]'" <[email protected]>
Date: Monday, March 14, 2011, 8:43 PM

What is the distance from the deck to the drop ceiling? The EC 11 heads are 
listed for unobstructed, combustible construction.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Monday, March 14, 2011 3:11 PM
To: [email protected]
Subject: RE: EC Upright in Attic Space

Yeah, but I'm looking at an 11.2K e/c at 18x18 in wood trusses.

--- On Mon, 3/14/11, Richard Carr <[email protected]> wrote:

From: Richard Carr <[email protected]>
Subject: RE: EC Upright in Attic Space
To: [email protected]
Date: Monday, March 14, 2011, 7:52 PM

THE Tyco CC2 head will let you do 144 sq. ft.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Monday, March 14, 2011 3:37 PM
To: [email protected]
Subject: EC Upright in Attic Space

I'm looking at some pre-designed fire sprinkler drawings showing extended 
coverage uprights in a concealed combustible space above a grid ceiling 
consisting of open web wood trusses (relatively no pitch) at 24" o/c. 

Looking at 8.4.3. (2007 ed) I don't think this is permissible mainly because of 
the "smooth, flat" criteria. Am I right? And does someone make an EC upright 
that can possibly be used in this scenario (besides the Tyco attic sprinklers).

Thanks,
 Ralph




      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely for the 
intended recipient(s). If you are not the named recipient you should not read, 
distribute, copy or alter this email. Any views or opinions expressed in this 
email are those of the author and do not represent those of the  company. 
Warning: Although precautions have been taken to make sure no viruses are 
present in this email, the company cannot accept responsibility for any loss or 
damage that arise from the use of this email or attachments.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to