Not to push any particular product or manufacturer, but several of the hose equipment manufacturers sell combination Flowmeter - Ventura setups for testing PRV's. One example is the model 9415 from Guardian Fire Equipment, Inc. http://www.guardianfire.com/products/sprinklertest/9415Flowmeter.html# I personally have never used one so I can't tell you the plumbing involved.
Richard L. Mote ET NICET Cert. No. 067611 Designer Rowe Sprinkler Systems, Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Macris, George Sent: Tuesday, March 22, 2011 9:04 AM To: [email protected] Subject: RE: PRV Testing This is a new sprinkler installation and having on site problems with testing of the PRVs for each floor in the building. The design engineer is not helpful and the installers have no clue of how to test them. Will you be able to describe how the actual test in done? I thought you also need to use a pitot tube, but how can this be done if you use a short piece of testing hose with one side connected to the drain riser and the other side just after the PRV. Thanks, George Macris,Plans Examiner/Fire Prevention Officer Markham Fire & Emergency Services 101 Town Centre Boulevard Markham, Ontario L3R 9W3 [email protected] www.markham.ca _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)