George,

The pitot tube is used only for testing and verifying flow through the flow 
meter before using the flow meter to test the PRV. The contractor can use an 2 
1/2 inch hose in-line pressure gauge coupled to a 2 1/2 inch in-line flow meter 
which is then connected to the 4 inch drain riser.  The testing  contractor can 
make two or three test set ups and pre-stage the testing of the PRV on the 
standpipe system. 

You might have to set up a demonstration for the AHJ for their review and 
approval. 

Regards

Jim 

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Macris, George
Sent: Tuesday, March 22, 2011 10:31 AM
To: [email protected]
Subject: RE: PRV Testing

Thanks Jim.
The test assembly as mentioned does it come with the flow meter and pitot tube? 
Is there any web sites I can look at?
Thanks for all the information.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Tuesday, March 22, 2011 9:56 AM
To: [email protected]
Subject: RE: PRV Testing

We have worked with owners of high rise building equipped with PRV's to upsize 
the drain risers to 4 inch and equipped with a 2½ swivel male inlet with valve 
to allow flow testing of PRV in place. The contractor usually uses a 2 1/2" 
flow meter, that has been flow tested and flow verified with a pitot tube and 
gauge, before testing in the high rise building, and places a pressure gauge on 
the inlet side of the PRV.  The installing contractor should have installed a ¼ 
inch tap with ¼ inch valve and plug on the PRV's inlet piping. Connect the test 
assembly to the PRV and to the drain riser and then flow test the PRV taking 
pressure reading from the supply side of the PRV and from the pressure gauge on 
the flow meter for the discharge side of the PRV.  Just make sure that the 4 
inch drain riser has some offsets in the vertical drop so the slug of water 
from the testing does not have a 600 ft straight drop to the first Ell. This 
test set up permits a contractor to adequately flow test the PRV's in a 
efficient manner with little of no damage to the contents of the building.  

Have a fire safe day.

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ford, Charles
Sent: Tuesday, March 22, 2011 9:30 AM
To: [email protected]
Subject: RE: PRV Testing

My original post was related to the pressure settings on existing PRV's. Don't 
need a pitot. Your question seems to acceptance testing of the stand pipes. 
Setting or verifying the PRV settings is part of the testing but it seems to me 
that full flow teating at the top is also required, but frankly I don't know 
exactly how that is done.   

C. Burton Ford
Nicet Certified
Special Hazards IV
Fire alarm IV
Sprinkler III
Water Based Inspections I
NFPA Certified Fire Protection Specialist [CFPS]
Cintas Fire Protection
1038 Conshohocken Road
Conshohocken ,PA 19428
610-233-1400
Fax 610-233-1401
________________________________________
From: [email protected] 
[[email protected]] On Behalf Of Macris, George 
[[email protected]]
Sent: Tuesday, March 22, 2011 9:03 AM
To: [email protected]
Subject: RE: PRV Testing

This is a new sprinkler installation and having on site problems with testing 
of the PRVs for each floor in the building. The design engineer is not helpful 
and the installers have no clue of how to test them. Will you be able to 
describe how the actual test in done? I thought you also need to use a pitot 
tube, but how can this be done if you use a short piece of testing hose with 
one side connected to the drain riser and the other side just after the PRV.

Thanks,


George Macris,Plans Examiner/Fire Prevention Officer
Markham Fire & Emergency Services
101 Town Centre Boulevard
Markham, Ontario L3R 9W3
[email protected]  www.markham.ca




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Eric Tysinger
Sent: Monday, March 21, 2011 3:37 PM
To: [email protected]
Subject: RE:

I have used a single 2½" female hose x male thread adapter, about a foot off 
the floor. Then you use a short piece of 2½" fire hose for testing.


Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, March 21, 2011 3:06 PM
To: [email protected]
Subject:

Tom,

Do you have a picture or a sketch of a drain riser and connections for a 2-1/2" 
pressure reducing hose valve? I'm having a hard time picturing how this all 
goes together. Also any hints on distance or arrangement would be helpful. 
Thanks

Todd

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
**************************************************************************************************

This e-mail contains information that may be privileged and/or confidential.  
If you are
not the intended recipient, any disclosure, distribution, copying or other use 
of this
e-mail or the information contained herein or attached hereto is strictly 
prohibited and
may be unlawful. If you have received this e-mail in error, please notify this 
sender
immediately and delete this e-mail without reading, printing, copying or 
forwarding it to
anyone. Thank you for your co-operation.

**************************************************************************************************

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.  Your assistance in correcting this 
error is appreciated.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
**************************************************************************************************

This e-mail contains information that may be privileged and/or confidential.  
If you are 
not the intended recipient, any disclosure, distribution, copying or other use 
of this 
e-mail or the information contained herein or attached hereto is strictly 
prohibited and 
may be unlawful. If you have received this e-mail in error, please notify this 
sender 
immediately and delete this e-mail without reading, printing, copying or 
forwarding it to 
anyone. Thank you for your co-operation.

**************************************************************************************************

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to