An offbeat code for actuating device trim for sprinks is NFPA 72(?), i.e,
not sure about size (does it matter?), but pipe type has to be
non-corrosive.

-----Original Message-----
From: Sean Lockyer [mailto:[email protected]] 
Sent: Thursday, March 24, 2011 1:16 PM
To: [email protected]
Subject: Air Maintenance Device Sizes

I have an odd situation that I have never seen before; I recently did an
inspection in which we had a faulty air maintenance device (Tyco AMD-1) and
the air maintenance device itself is 1/2" but the piping back to the AMD to
the dry pipe valve was 1/4" (it was reduced down immediately from the
connection). Per the listing isn't the piping required to be a minimum of
1/2" ? In addition, is there an code reference requiring the AMD line to be
a minimum size ?

Lastly, there was another AMD for a model that I have heard of, it is a
Parker Filtration Model RP FR-1004CSS. I searched high and low in the land
of Google but could not find anything; the closest I found was an Air Gap
that was for a different model number. I wonder if this is a type of AMD but
is not actually listed for fire sprinkler use and that the problems in the
dry system is not the valves or the other AMD but is in fact this off-brand
type.

What says the community ?

-- 
Sean Lockyer
Project Designer
Delta Fire Sprinklers
(407) 328-3000, ext 139
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to