AMD and air regulator are not synonymous. Some AMDs have regulators
but no regulator would be a listed AMD assembly.

On Thu, Mar 24, 2011 at 12:34 PM, Roland Huggins
<[email protected]> wrote:
> you can also do an online search of the UL directory for listed products.
>
> Roland
>
> On Mar 24, 2011, at 11:16 AM, Sean Lockyer wrote:
>
>> I have an odd situation that I have never seen before; I recently did an
>> inspection in which we had a faulty air maintenance device (Tyco AMD-1)
>> and
>> the air maintenance device itself is 1/2" but the piping back to the AMD
>> to
>> the dry pipe valve was 1/4" (it was reduced down immediately from the
>> connection). Per the listing isn't the piping required to be a minimum of
>> 1/2" ? In addition, is there an code reference requiring the AMD line to
>> be
>> a minimum size ?
>>
>> Lastly, there was another AMD for a model that I have heard of, it is a
>> Parker Filtration Model RP FR-1004CSS. I searched high and low in the land
>> of Google but could not find anything; the closest I found was an Air Gap
>> that was for a different model number. I wonder if this is a type of AMD
>> but
>> is not actually listed for fire sprinkler use and that the problems in the
>> dry system is not the valves or the other AMD but is in fact this
>> off-brand
>> type.
>>
>> What says the community ?
>>
>> --
>> Sean Lockyer
>> Project Designer
>> Delta Fire Sprinklers
>> (407) 328-3000, ext 139
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to