Really it doesn't matter what NFPA intends.  You are correct legally it
doesn't apply to older codes.  Probably doesn't legally apply to the 2010
unless specifically adopted by the jurisdiction.  Jurisdictions usually have
processes to adopt law that don't defer to NFPA.  NFPA doesn't make law.  A
fire marshal can't write an order to follow the TIA.  That's the legal
matter.  On the civil side, like a loss of any kind, you the fire marshal
will not be issuing a ticket but the contractor will be served civil papers
by the insurance company that paid on the loss.  There it is up to who has
the better lawyer and/or which side fights the longest to find out if it
applies in that case.  Different cases, different judges, different
insurance companies will have different outcomes. 

Chris

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dave Phelan
Sent: Saturday, March 26, 2011 7:32 AM
To: [email protected]
Subject: Antifreeze TIA Applicability?

As I read the TIA's and supporting documents on the antifreeze issue I see
they all reference the 2010 editions of the NFPA Sprinkler standards.

What impact does these NFPA TIA's have on any prior editions?  If any -

I'm asking because this state is currently using the 2007 editions under the
2009 IBC . So when a TIA is issued on the current NFPA edition does NFPA
intend for it to have any effect on the prior editions which may very well
be the prevailing codes in a state / jurisdiction?  My gut tells me it
doesn't apply to other editions unless they specifically make that
stipulation but that wouldn't necessarily change the science of the problem.

Thoughts?

 

Dave P. in NJ

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to