OK I sent the question to the Arch/Engineer and they said they want to use
wet SW's and if only the head is outside and pipe is in an insulated wall it
won't freeze(?!?!?!). So now I need to find an EC SW listed for storage that
will throw 16' under one canopy and 22'-0 under the other. Of course I
cannot find one; any know of any I might be overlooking?

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, March 28, 2011 11:19 AM
To: [email protected]
Subject: RE: Extended Coverage Dry SW for STORAGE

 

If it's in the spec you need to provide it.  What's the problem?

Seriously, if it's storage they should have considered a dry system based on
the depth of the area. 

The walkway, not enough info. If it's just a convenience walkway and not
part of a required egress path, constructed of non-combustible components,
not designed to accommodate any storage and separated from the occupied part
of a building by a non-combustible separation it PROBABLY won't require to
be sprinklered but more info would have to be shared to render a more
substantial yeah or nay.

Craig L. Prahl, CET  
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Saturday, March 26, 2011 1:58 PM
To: [email protected]
Subject: Exteneded Coverage Dry SW for STORAGE

Anyone heard of one of these? Project we r bidding is asking for Dry
sidewalls for exterior storage canopies - one is 22'-0 deep and the other is
16'-0. The best I could find was an EC Dry SW for OH that throws up to
20'-0. I believe they need a dry system for each one.



While I am at it they have a "covered walkway" (as its labeled) 11'-6 deep
attached to building - not requesting sprinklers but I feel they will have
to it. What say ye?



Thanks,



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]







_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1204 / Virus Database: 1498/3535 - Release Date: 03/28/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to