Not at this point; they don't want a dry system and want wet SW's. They
haven't said what the storage criteria is but said to protect it at .3/2500.


 

 

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, March 28, 2011 12:27 PM
To: [email protected]
Subject: RE: Extended Coverage Dry SW for STORAGE

 

Bad idea.  Guess they won't back up on their concept of SW's huh?

Whether the head will transmit enough cold to cause a freezing condition
inside depends on the climate.  But I wouldn't put any money on it unless
you were in S. Texas, Arizona, Fla or So. Cal.

Just curious but what density did they call out for the storage area?  Did
they list what materials were being stored or just pick a "it felt good"
Hazard category from NFPA 13?

Craig L. Prahl, CET  
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Monday, March 28, 2011 1:20 PM
To: [email protected]
Subject: RE: Extended Coverage Dry SW for STORAGE

OK I sent the question to the Arch/Engineer and they said they want to use
wet SW's and if only the head is outside and pipe is in an insulated wall it
won't freeze(?!?!?!). So now I need to find an EC SW listed for storage that
will throw 16' under one canopy and 22'-0 under the other. Of course I
cannot find one; any know of any I might be overlooking?



Thank you,



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]





  _____ 

From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, March 28, 2011 11:19 AM
To: [email protected]
Subject: RE: Extended Coverage Dry SW for STORAGE



If it's in the spec you need to provide it.  What's the problem?

Seriously, if it's storage they should have considered a dry system based on
the depth of the area.

The walkway, not enough info. If it's just a convenience walkway and not
part of a required egress path, constructed of non-combustible components,
not designed to accommodate any storage and separated from the occupied part
of a building by a non-combustible separation it PROBABLY won't require to
be sprinklered but more info would have to be shared to render a more
substantial yeah or nay.

Craig L. Prahl, CET 
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Saturday, March 26, 2011 1:58 PM
To: [email protected]
Subject: Exteneded Coverage Dry SW for STORAGE

Anyone heard of one of these? Project we r bidding is asking for Dry
sidewalls for exterior storage canopies - one is 22'-0 deep and the other is
16'-0. The best I could find was an EC Dry SW for OH that throws up to
20'-0. I believe they need a dry system for each one.



While I am at it they have a "covered walkway" (as its labeled) 11'-6 deep
attached to building - not requesting sprinklers but I feel they will have
to it. What say ye?



Thanks,



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]







_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

  _____ 

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1204 / Virus Database: 1498/3535 - Release Date: 03/28/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1204 / Virus Database: 1498/3535 - Release Date: 03/28/11

_______________________________________________