Look at table 12.3.2.4.2.1.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sean
Lockyer
Sent: Tuesday, March 29, 2011 3:14 PM
To: [email protected]
Subject: In-rack sprinkler maximum and minimum spacing...

I have a fire marshal wanting me to show him where in NFPA 13 it
dictates
the minimum and maximum spacing of in-rack sprinklers. This is a good
question, for the life of me I have never found it in black and white. I
know that there are several references to 8'-0" maximum spacing per
sprinkler for storage up to 25'-0" but we are only storing up to 20'-0".

I have always been under the impression that you space a sprinkler in
each
in-rack flue space, usually on the center point of the rack or at the
rack
upright. Normally the racks are spaced around 8'-0" O.C. but there is
one
here that is 4'-0" O.C. We are using intermediate level in-rack
sprinklers
with the overhead system being ELO sprinklers-no ESFR, Large Drop,
etc...

We are using NFPA 13, 2002 Edition here in Florida. What says the
community
?

-- 
Sean Lockyer
Project Designer
Delta Fire Sprinklers
(407) 328-3000, ext 139
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely for the 
intended recipient(s). If you are not the named recipient you should not read, 
distribute, copy or alter this email. Any views or opinions expressed in this 
email are those of the author and do not represent those of the  company. 
Warning: Although precautions have been taken to make sure no viruses are 
present in this email, the company cannot accept responsibility for any loss or 
damage that arise from the use of this email or attachments.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to