To avoid someone form dancing on that thin ice, the cut sheet identifies the equivalent length of the device but then introduces some ambiguity by saying: The hydraulic loss of the Flexhead connector needs to be included in the hydraulic design calculations the same as a valve OR FITTING. Was doing fine until the last two words since as you pointed out, 13 says ignore the FITTING that is directly connected to a sprinkler. Calling it a connector helps indicate the intent.

Roland

On Apr 5, 2011, at 2:17 PM, Todd Williams wrote:

Hey Roland, Since section 22.4.4.7(9) states that we can ignore the fitting attached to the sprinkler and a Flexhead is considered a fitting and is attached to the head, can the friction loss in it be ignored?

_______________________________________________