in all seriousness,
why can't TD
do a "bucket test"         ;-)

or in the least, pitot the main drain flow?
Below are a couple of ways to go.

1.  Bucket test would take the drain from the main
into some big storage thing and count the gallons
over...say 30 seconds,  that is Q.  Done.  You got
Pstatic, Presidual, and Q, at a point near the BoR.

Don't know what kind of "big storage thing"  you are going to use,
but that approach is what I would chose,
rather than an application of Bernoulli's that was misused.

2.  take a low volume pitot to the main drain discharge and
get Q that way.

3.  Use Bernoullis anyway, but apply it properly.

P1       static pressure at gauge
v1       zero
h1       height at gauge (not ceiling)

P2      residual pressure at gauge
v2      what we be looking to solve (can be cross checked with low volume
pitot)
h2      height at gauge

we could alternatively take another location on the streamline as our point
"2"
and drop all consideration to the bucket test/pitot flow.

P2     0 psi gauge pressure at main drain discharge
v2     what we solve for (and cross check by low volume pitot)
h2     height at main drain discharge


scot deal
excelsior fire engineering

P.S.  How accurate is the pressure gauge on the riser/main drain anyway?



On Wed, Apr 6, 2011 at 1:17 AM, Todd Williams <[email protected]> wrote:

> Uh.....
>
> I'm not sure Brad's assumptions on the flow are valid. V = sqrt(2gh) is for
> an object in free fall, discounting any friction or drag. I don't think you
> can apply it to discharge through an orifice.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to