translated to:

NFPA 13R does not require the breezeway to be protected and the IBC does not impose additional requirements (since a breezeway is not a rare feature and it is NOT a balcony, deck or patio).

Roland

On Apr 6, 2011, at 6:19 PM, John Drucker wrote:

2009 IBC/IFC  (Model Code - Not Jurisdiction Specific)

[F] 903.2.8 Group R. An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R
fire area.

[F] 903.3.1.2 NFPA 13R sprinkler systems. Where allowed in buildings of Group R, up to and including four stories in height, automatic sprinkler
systems shall be installed throughout in accordance with NFPA 13R.

2007 NFPA-13R

4.3 Basic Requirements.
4.3.1 The requirements for spacing, location, and position of sprinklers
shall be based on the following principles:

(1) Sprinklers shall be installed throughout the premises.
(4) Sprinklers shall be permitted to be omitted from areas specifically
allowed by this standard (see Section 6.9).

6.9 Location of Sprinklers.

6.9.1 Sprinklers shall be installed in all areas except where omission is
permitted by 6.9.2 through 6.9.7.

6.9.5 Sprinklers shall not be required in any porches, balconies, corridors,
and stairs that are open and attached.

_______________________________________________________________
13R-19 Log #19 AUT-RSS Final Action: Accept in Principle
(6.9.5)
Submitter: Phillip A. Brown, American Fire Sprinkler Association, Inc.
Comment on Proposal No: 13R-44
Recommendation: Add new text to read as follows:

A.6.9.5 An example of an open corridor or breezeway is one that empties to an outside stairway and has no doors attached to it. Another example is an exterior wraparound corridor that is typical in a two- to three- story motel. Substantiation: Guidance is needed to help explain what the word "open" means as used in 6.9.5. The comment found in the Handbook helps explain
what "open" means and should be brought forward into the annex.
Committee Meeting Action: Accept in Principle
Revise proposal to read as follows:

A.6.9.5 An example of an open corridor or breezeway is one that is exposed
to
the outside atmosphere (temperature) and empties to an unenclosed stairway and has no doors attached to it. Another example is an exterior wraparound
corridor that is typical in a two- to three-story motel.
Committee Statement: Further clarifies the intent of the committee and the
standard in defining an open corridor.
Number Eligible to Vote: 25
Ballot Results: Affirmative: 23 Negative: 1
Ballot Not Returned: 1 Schirmer, C.
Explanation of Negative:
HAAGENSEN, D.: In the Northeast, there are many situations where a porch/
balcony may be almost entirely enclosed except for some small screened
windows, thereby creating a space where heated fire gases during a fire will build up and not allow for tenability in the space. The guidance given in
the
new Annex will suggest that such a space is "open".

2009 IBC/IRC

[F] 903.3.1.2.1 Balconies and decks. Sprinkler protection shall be provided for exterior balconies, decks and ground floor patios of dwelling units
where the
building is of Type V construction, provided there is a roof or deck above. Sidewall sprinklers that are used to protect such areas shall be permitted to be located such that their deflectors are within 1 inch (25 mm) to 6 inches (152 mm) below the structural members and a maximum distance of 14 inches (356 mm) below the deck of the exterior balconies and decks that are
constructed of open wood joist construction.

102.1 General. Where there is a conflict between a general requirement and a specific requirement, the specific requirement shall be applicable. Where, in any specific case, different sections of this code specify different
materials, methods of construction or other requirements, the most
restrictive shall govern.

102.4 Referenced codes and standards. The codes and standards referenced in this code shall be considered part of the requirements of this code to the prescribed extent of each such reference. Where differences occur between provisions of this code and referenced codes and standards, the provisions
of this code shall apply.

104.1 General. The building official is hereby authorized and directed to enforce the provisions of this code. The building official shall have the authority to render interpretations of this code and to adopt policies and
procedures in order to clarify the application of its provisions. Such
interpretations, policies and procedures shall be in compliance with the intent and purpose of this code. Such policies and procedures shall not have
the effect of waiving requirements specifically provided for in this
code.

Hope this helps,

John Drucker, CET

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to