If the property were FM insured it's possible the concern comes from the fact 
that FM does not list any concealed sprinkler as quick response.  Since light 
hazard requires the use of QR sprinklers thats a possible limitation, I haven't 
dug deeply enough to find out if the fact that some concealed sprinklers that 
are FM listed as SR are UL listed as QR still allows the use of LH design 
parameters, a quick look isn't showing anything to override the requirements of 
13 in that regard, but we don't deal with much non-storage work so I'm not as 
familiar with FM's interaction with 13 on the subject, it appears they yield 
most of this to standard 13 design.
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com

________________________________

From: [email protected] on behalf of Bill Brooks
Sent: Fri 4/8/2011 11:01 AM
To: [email protected]; [email protected]
Subject: RE: Concealed Sprinklers Limited to Ordinary Hazard Spacing



In other words, a light hazard occupancy with two different areas of
coverage depending on the type of head?  Sounds like the engineer is
concerned about the response time of the concealed heads vs the recessed.
Maybe he/she attended a recent performance design seminar and doesn't
realize we are dealing with rules and not engineering design.  Are the
concealed installed at a higher elevation than the recessed?  NFPA 72
adjusts detector spacing for ceiling height, but so far NFPA 13 does not
build this in.   Are you in charge of selecting the sprinkler type?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike Hill
Sent: Friday, April 08, 2011 9:39 AM
To: [email protected]
Subject: Concealed Sprinklers Limited to Ordinary Hazard Spacing

This may have been covered in the past, but I did not see any mention of it.



Recently we have seen contract specifications requiring that concealed
sprinklers be spaced for ordinary hazard requirements, while allowing
recessed sprinklers to be spaced for light hazard requirements in the same
space. Does anyone know where this requirement may be coming from? Want to
make sure I didn't something.



Michael Hill

Vice President



Phoenix Fire Protection, Inc.

(301) 669-7066



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to