Bobby, I am on the road so I didn't look this up but last week I was looking
up some criteria for storage and was referred back to the criteria for misc.
Storage.

So maybe that's what is happening?
On Apr 11, 2011 6:44 AM, "Bobby Gillett" <[email protected]>
wrote:
> Matt,
>
> Thank you and I agree. That’s why I was asking - they had the key words
> leading to retail storage but they specifically call out the sprinklers
and
> the Table for Misc Storage in their specs.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Matt Grise
> Sent: Monday, April 11, 2011 6:18 AM
> To: '[email protected]'
> Subject: RE: Retail Store Design
>
> It sounds like they are looking for the retail requirements - especially
> since they use the term 'gondola racks'. Also, Misc storage is limited to
> 4000 sf and is supposed to be 'incidental to another occupancy use'. Also,
> if you go with the standard storage criteria for racks with solid shelves,
> you will have in-rack sprinklers.
>
> Matt Grisé PE*, LEED AP
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bobby
Gillett
> Sent: Sunday, April 10, 2011 12:40 PM
> To: [email protected]
> Subject: Retail Store Design
>
> I am working on system design for a major retail chain for office
products;
> Top of steel is 19'-0 high, exposed structure - their specs call for
> standard response brass upright 286° sprinklers and say the following:
>
>
>
> A. "All fire protection systems for the entire retail sales and receiving
> areas shall meet the requirements for storage of commodities in single row
> and double row racks as well as solid shelf gondola racks which have an
> overall width greater than 30 inches and for storage of commodities to a
> maximum height of 12'-0 AFF." And then refers to NFPA 13 2002 Table
> 12.1.10.1.1. (which is Misc Storage up to 12' in height).
>
>
>
> E. " The sprinkler system for the entire retail sales and receiving areas
> shall be designed in accordance with NFPA 13 requirements for gondola
> storage greater than 30 inches in overall width, which are treated as
racks
> with solid shelving, in addition to single and double row rack storage of
> Class I-IV non-encapsulated commodities to an overall height of 12'-0 AFF.

>
>
>
> According to their specs, it appears they are applying NFPA 13 -2002 Misc
> storage 12.1.10 (Chapter 13 in NFPA 2007). My question is - When do you
> apply NFPA 13 2002 - 12.7.2 (NFPA 13 2007 - 20.3)? Would the scenario
above
> apply to these chapters or would it be Misc Storage?
>
>
>
> Thank you,
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office (731) 424-9285 fax
>
> (731) 267-4853 cell
>
> <mailto:[email protected]>
> [email protected]
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1321 / Virus Database: 1500/3565 - Release Date: 04/11/11
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to