Thanks, George.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, April 11, 2011 2:53 PM
To: [email protected]
Subject: RE: Retail Store Design

http://www.tyco-fire.com/index.php?P=show&B=&CP=1&id=EC25WP_03_2011&BK=lit&B
L=Technical Reports and White Papers
http://www.tyco-fire.com/index.php?P=lit&L=Technical Reports and White
Papers&B=

chk with your TFP local guy for more, I've seen some brand-specific
write-ups but I don't know how close you alignment is.

If you haven't read James' white paper on Variables that affect the
performance of a dry pipe system, you should in order to really understand
how increasing air pressure in a dry sysem gievs better results, while
others are offering low pressure valves that trip faster, but at extended
transit times since there's less air stopping water from being diverted from
the ITC/flowing heads..while you're looking at the index, take some time and
educate yourself. If you have, understand a lot on the Forum prolly haven't.
What I learned from Design Alternatives for Large Drops got me a $1.7m job,
so don't necessarily think you're wasting your time.

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
Sent: Monday, April 11, 2011 12:54 PM
To: [email protected]
Subject: RE: Retail Store Design

You may want to look at the Office depot and other special application
sprinkler criteria that TYCO developed along with major retail outlets. I
believe that Bed bath and beyond and others were provided with testing to
support specific ceiling only sprinkler protection.
These are now most likely listed as CMSA sprinklers, but I think the white
papers are still available on the TYCO web page.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Monday, April 11, 2011 7:17 AM
To: [email protected]
Subject: RE: Retail Store Design

Greg,

Section 16 (Rack storage) will send you back to Misc Storage. That was the
confusing part. This is a mercantile occupancy with a small area of storage
in receiving not exceeding 12'-0 in height. They have gondola shelves on the
sales floor (most of it) - not exceeding 12'-0 in height & the highest point
of Top of Steel is 19'-0. Their specs are building it towards Misc Storage
including types of sprinklers and referenced Table (12.1.10.1.1 in 2002) So
with that said - which way to go? 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Monday, April 11, 2011 7:55 AM
To: [email protected]
Subject: RE: Retail Store Design

Bobby, I am on the road so I didn't look this up but last week I was looking
up some criteria for storage and was referred back to the criteria for misc.
Storage.

So maybe that's what is happening?
On Apr 11, 2011 6:44 AM, "Bobby Gillett" <[email protected]>
wrote:
> Matt,
>
> Thank you and I agree. That's why I was asking - they had the key 
> words leading to retail storage but they specifically call out the 
> sprinklers
and
> the Table for Misc Storage in their specs.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office (731) 424-9285 fax
> (731) 267-4853 cell
> [email protected]
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Matt 
> Grise
> Sent: Monday, April 11, 2011 6:18 AM
> To: '[email protected]'
> Subject: RE: Retail Store Design
>
> It sounds like they are looking for the retail requirements - 
> especially since they use the term 'gondola racks'. Also, Misc storage 
> is limited to
> 4000 sf and is supposed to be 'incidental to another occupancy use'. 
> Also, if you go with the standard storage criteria for racks with 
> solid shelves, you will have in-rack sprinklers.
>
> Matt Grisé PE*, LEED AP
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bobby
Gillett
> Sent: Sunday, April 10, 2011 12:40 PM
> To: [email protected]
> Subject: Retail Store Design
>
> I am working on system design for a major retail chain for office
products;
> Top of steel is 19'-0 high, exposed structure - their specs call for 
> standard response brass upright 286° sprinklers and say the following:
>
>
>
> A. "All fire protection systems for the entire retail sales and 
> receiving areas shall meet the requirements for storage of commodities 
> in single row and double row racks as well as solid shelf gondola 
> racks which have an overall width greater than 30 inches and for 
> storage of commodities to a maximum height of 12'-0 AFF." And then 
> refers to NFPA 13 2002 Table 12.1.10.1.1. (which is Misc Storage up to 12'
in height).
>
>
>
> E. " The sprinkler system for the entire retail sales and receiving 
> areas shall be designed in accordance with NFPA 13 requirements for 
> gondola storage greater than 30 inches in overall width, which are 
> treated as
racks
> with solid shelving, in addition to single and double row rack storage 
> of Class I-IV non-encapsulated commodities to an overall height of 12'-0
AFF.

>
>
>
> According to their specs, it appears they are applying NFPA 13 -2002 
> Misc storage 12.1.10 (Chapter 13 in NFPA 2007). My question is - When 
> do you apply NFPA 13 2002 - 12.7.2 (NFPA 13 2007 - 20.3)? Would the 
> scenario
above
> apply to these chapters or would it be Misc Storage?
>
>
>
> Thank you,
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office (731) 424-9285 fax
>
> (731) 267-4853 cell
>
> <mailto:[email protected]>
> [email protected]
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1321 / Virus Database: 1500/3565 - Release Date: 
> 04/11/11
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1321 / Virus Database: 1500/3565 - Release Date: 04/11/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1321 / Virus Database: 1500/3565 - Release Date: 04/11/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to