Another one that gets me is in 13R is that distance away from the obstructions 
are now measured from the centerline of the obstruction instead of the edge 
like 13.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Monday, April 11, 2011 9:30 PM
To: [email protected]
Subject: Re: NFPA 13(07) vs 13R(07)

I was hoping foe an answer to this myself. I'm guessing it's just an anomaly 
between two different committees but your guess might also be right.

On Mon, Apr 11, 2011 at 1:45 PM, Dewayne Martinez <[email protected]> wrote:
> I am a bit confused when looking over the rules for ceiling fans and 
> residential sprinklers.
> NFPA 13 section 8.10.7.2.1.7 allows the blades of the fan to be 
> ignored for Res HSW sprinklers while NFPA 13R section 6.8.1.5.3.3 (A) 
> requires that the Res HSW sprinklers be at least 5ft away from a 
> ceiling fan.
> Why would this be different for the same type of sprinkler?  Is is 
> because 13 requires 0.10 gpm/sqft vs 13R 0.05 gpm/sqft?
> Thanks,
> Dewayne Martinez
> Design Build Fire Protection
> New Berlin, WI
> <http://www.designbuildfire.com/>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to