PC 3 labs are 'totally clean' and have sealed walls/floors/ceilings. Could make 
drainage a problem - you might have to consider floor drains with covers which 
would have to be removed after actuation.  Of course, this is a good example of 
an application for a high pressure (>200 bar) mist system using cylinders an 
ultra clean water.

Stewart
On 15 Apr 2011, at 14:26, George Church wrote:

> Just as a crazy idea, for a little self-contained box where you have a 
> problem with contaminated water runoff, could you limit the amount by using a 
> 13D tanka nd puimp so you have x gallons to discharge, hopefully knock it 
> down, and get everyone out, then the water in the tank runs out and that's 
> the end of it. Small pressure tank would give more robustness, compliance 
> with 13/22, or a simpler well tank would be cost effective, not need 
> electric, and be more reliable than a 13d pump.
> 
> Concept I'm pushing is to limit amount of water. Floor drains might be piped 
> to a poly holding tank?
> 
> George Church
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Friday, April 15, 2011 8:42 AM
> To: [email protected]
> Subject: RE: PC- 3 Laboratories
> 
> PC means Physical Containment, the 3 is the designation on a scale of 1-4.  A 
> Level 3 lab is typically for biological research/testing.  Think of stuff 
> like Ebola or other "bad bugs", stuff you don't want to escape into the 
> atmosphere.  These labs are under negative pressure and have air locks for 
> entering and leaving.  Stringent decontamination requirements are also in 
> place.
> 
> Sprinklers will pose a problem in that anything leaving the lab has to be 
> decontaminated.  There would have to be floor drains in the lab to capture 
> the sprinkler discharge and route it to a containment area where is can be 
> decontaminated.  It can get complicated since the effluent must be fully 
> contained to prevent it's escape into the atmosphere prior to 
> decontamination.  Standard floor drains can't be used due to the negative 
> pressure issue so they create an added expense beyond normal floor drains.
> 
> So the Client who says no sprinklers may be on the right track.  Another 
> means of protection may be more suitable and water may not be compatible with 
> the materials being tested in the lab.  You need a chemicals inventory list 
> and the lab's procedures for handling and storage.  Depending on where this 
> lab is being built portable fire extinguishers maybe all that's needed.  This 
> maybe a case where fire prevention procedures have to take the lead due to 
> safety and environmental issues instead of going the standard route of 
> sprinklering the lab.
> 
> You need to do some serious homework before just throwing sprinklers in the 
> place.
> 
> Craig L. Prahl, CET   
> Fire Protection 
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Chris Mak
> Sent: Thursday, April 14, 2011 7:09 PM
> To: [email protected]
> Subject: PC- 3 Laboratories
> 
> I have a client who is being challenged by his client as not to put 
> sprinklers into a PC-3 (Physical Containment Level 3) laboratory.
> 
> I am uncertain about the designation - the laboratory is being built and 
> certified in Europe before being shipped here to be installed within a  
> building here on the other side of the globe. Hence, PC-3  may be a European 
> designation and not an American designation.
> 
> Apparently, the laboratory will be occupied by three people - i.e. it's not a 
> small cupboard or fume hood sized.
> 
> Any experiences in protecting, or not protecting such laboratories?
> 
> 
> Thanks
> 
> 
> 
> Chris Mak | Aon New Zealand
> Sprinkler Certification Manager
> Level 1, 4 Fred Thomas Drive,;PO Box33-1240 Takapuna
> t: +6494869761 | f: +6494860112 | m: +64274344058
> e: [email protected]
> 
> Please consider the environment before printing this email.
> 
> 
> 
> 
> 
> 
> This communication (and any attachments) is directed in confidence to the 
> addressee(s) listed above, and may not otherwise be distributed, copied or 
> used. The contents of this communication may also be subject to privilege, 
> and all rights to that privilege are expressly claimed and not waived. If you 
> have received this communication in error, please notify us by reply e-mail 
> or by telephone and delete this communication (and any attachments) without 
> making a copy.
> 
> Before opening or using attachments, you should check them for viruses and 
> defects. We do not accept liability in connection with computer virus, data 
> corruption, delay, interruption, unauthorised access or unauthorised 
> amendment.
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to