I'd say the annex material in NFPA 13 2010 A.8.17.4.2 suggesting locating wet 
system test connections at the riser to eliminate the introduction of air into 
the system would be one reason to believe they may be on to something.  They 
aren't the only company moving in this direction.  Also we've had some alarm 
issues on a particular building we service and several manufacturers who have 
no stake in the "air vent" business immediately suggested trapped air was a 
concern.  The installation of air vents has dropped the alarm test time from 
about 1 minute to about 30 seconds...  On a system with large sections of 
trapped piping at least, they're definitely worth looking at.
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com

________________________________

From: [email protected] on behalf of [email protected]
Sent: Fri 4/15/2011 1:24 PM
To: [email protected]
Subject: Automatic Air Vents



What is the forum's opinion in regard to the Potter Air Vent and Automatic
Air Release that they are hawking to preserve wet pipe sprinkler systems by
venting the trapped air at the top of the systems?  Their website is
http://www.pottersignal.com/news_sprinkler_PAVPAARB.aspx.  I don't see the
value.

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Cell - 817-371-3102

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to