I replied to Chris offline with specific details - we had a biotechnology 
research move into an old warehouse. They have multiple BL2 labs and two BL3 
labs. A BL3 lab can contain some serious bugs, generally infectious aerosols. 
Think more like SARS or West Nile, not Ebola. The truly bad stuff goes to BL4. 
The BL2 labs are Hep B, MRSA, mumps, dengue fever, at the like.

We were able to adequately address all of the issues using the information from 
the NIH Office of Research Facilities. They have specific design criteria here:

http://orf.od.nih.gov/PoliciesAndGuidelines/BiomedicalandAnimalResearchFacilitiesDesignPoliciesandGuidelines/DRMHTMLver/DesignRequirementsManualTableofContents.htm

Interestingly, when you look at specific fire code requirements, biohazards 
aren't included. They are not fire/chemical hazards. It took some maneuvering 
to pull out the proper code sections for the facility.

Jim K.



James M. Kettler, EFO, CFPS
Director of Building and Codes/Fire Marshal
Buckingham Township
PO Box 413
4613 Hughesian Drive
Buckingham, PA   18912
215-794-8836
www.buckinghampa.org





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, April 15, 2011 9:27 AM
To: [email protected]
Subject: RE: PC- 3 Laboratories

Just as a crazy idea, for a little self-contained box where you have a problem 
with contaminated water runoff, could you limit the amount by using a 13D tanka 
nd puimp so you have x gallons to discharge, hopefully knock it down, and get 
everyone out, then the water in the tank runs out and that's the end of it. 
Small pressure tank would give more robustness, compliance with 13/22, or a 
simpler well tank would be cost effective, not need electric, and be more 
reliable than a 13d pump.

Concept I'm pushing is to limit amount of water. Floor drains might be piped to 
a poly holding tank?

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to