I do not know of any code that says you must take them out. I would however
either take them all out or leave them all in. Do not leave an area that
does not meet code  (or could be easily confused as not meeting code).
Leaving a few of the uprights can give the 'illusion' of a non-compliant
system. 

That was advice I received 25 years ago and I still practice it.

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Tuesday, April 19, 2011 2:02 PM
To: [email protected]
Subject: RE: Tenant finish and existing sprinklers

Thanks Dale,
Since sprinklers are not required in this space per code, why couldn't you
leave some in?  You are still complying with code.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dale Wingard
Sent: Tuesday, April 19, 2011 11:49 AM
To: [email protected]
Subject: RE: Tenant finish and existing sprinklers

Dewayne,

IBC 901.2(2006) allows for a non required system to be installed or remain
as it exists, but it is required to meet the code requirements.
If you remove any uprights then you will need to remove all of them that are
located in the non combustible concealed space.

Dale F. Wingard, SET
Design Manager
Triple "A" Fire Protection, Inc.
251.649.2034
[email protected]

 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Tuesday, April 19, 2011 11:27 AM
To: [email protected]
Subject: Tenant finish and existing sprinklers

I think this was talked about but I couldn't find it in the archives.
I have a noncombustible tenant spec building that currently has upright
sprinklers installed.
I am going to use the existing sprinkler outlets to supply the areas with
finished ceilings.
Is there somewhere in NFPA or IBC/IFC that requires the existing upright

sprinklers to be removed and plugged from the finished ceiling areas if I
don't use the outlet?
 
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to