Ok, so why NOT leave them in there in case for some reason they are NEEDED (as 
opposed to required)?
Doesn't make sense (except as you noted, an illusion of coverage) to spend 
money to remove protection. 
A couple years from now they could have a roof leak, tiles are pulled, a week 
later they're about to replace them with new but- there's a fire. 
In my building, the uprights remaining control it.
In your building, you paid someone to remove what could have controlled the 
fire.

Would an SSU or CC2 every so often (but exceeding listed spacing) function as a 
detector to indicate an allowable unprotected combustible concealed space is on 
fire when you're running CPVC in a 13R wood truss building? Is that a bad thing 
we should never do? 

I may not be required to have a fire extinguisher in my house, but I do; couple 
of em. Should I remove them unless I'm going to completely blanket the house 
with FE's in accordance with applicable NFPA FE standards, even if inapplicable 
to my home? After all, my home is a "jobsite" since we replaced the GBs in it 
(installed by previous owner) so there's a blurring of what is and isn't "real" 
protection requirements, we can't play pretend with "just houses" any longer. 

If the 13D system in my home has a dry spot I can't reach (breakfast nook) 
without exposing it to freezing so its ignored, should I plug off all other 
heads so there's no illusion of FULL protection in the home? Or am I better off 
with protection throughout the house (even in some bathrooms <55 SF) knowing I 
will still get an alarm, somewhat delayed response from a HSW, and know I have 
egress paths I can use to get out if the breakfast nook is engulfed? My 13D was 
installed by previous owner voluntarily. Code nazi will improve society and my 
welfare by making me plug all the heads if he sees the "violation"? 

If that's the case, cops pulling u over for a broken headlight will break the 
remaining one so you know you need to get em fixed, right? And stop u from 
driving home with less than full lighting....

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mike Hill
Sent: Tuesday, April 19, 2011 2:54 PM
To: [email protected]
Subject: RE: Tenant finish and existing sprinklers

I do not know of any code that says you must take them out. I would however 
either take them all out or leave them all in. Do not leave an area that does 
not meet code  (or could be easily confused as not meeting code).
Leaving a few of the uprights can give the 'illusion' of a non-compliant 
system. 

That was advice I received 25 years ago and I still practice it.

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Tuesday, April 19, 2011 2:02 PM
To: [email protected]
Subject: RE: Tenant finish and existing sprinklers

Thanks Dale,
Since sprinklers are not required in this space per code, why couldn't you 
leave some in?  You are still complying with code.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dale Wingard
Sent: Tuesday, April 19, 2011 11:49 AM
To: [email protected]
Subject: RE: Tenant finish and existing sprinklers

Dewayne,

IBC 901.2(2006) allows for a non required system to be installed or remain as 
it exists, but it is required to meet the code requirements.
If you remove any uprights then you will need to remove all of them that are 
located in the non combustible concealed space.

Dale F. Wingard, SET
Design Manager
Triple "A" Fire Protection, Inc.
251.649.2034
[email protected]

 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Tuesday, April 19, 2011 11:27 AM
To: [email protected]
Subject: Tenant finish and existing sprinklers

I think this was talked about but I couldn't find it in the archives.
I have a noncombustible tenant spec building that currently has upright 
sprinklers installed.
I am going to use the existing sprinkler outlets to supply the areas with 
finished ceilings.
Is there somewhere in NFPA or IBC/IFC that requires the existing upright

sprinklers to be removed and plugged from the finished ceiling areas if I don't 
use the outlet?
 
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to