>Hello Folks.
>Here in Monterrey Mexico we are designing a sprinkler system for a
>flammable liquid storage inside cut-off room. The design should be FM
>Global approve. And I want you to help me with the design
>criteria/specification. I want to use a close head wet sprinkler system
>with foam AFFF.
>
>Description:
>Flammable Liquids in Plastic Containers
>Container size: less than 14 gal.
>
>Storage Arrangement: Palletized only
>Roof Height: 15'
>Flash point:
>       Lemon oil: 125ºF
>       Vanilla flavor: 64.4ºF
>
>
>Searching on FM DS 7-29, Table 15, less than 200ºF, inside cut-off, not
>miscible, cut not be protected. But in the same table if I get it as
>miscible, I found:
>K11.2 QR
>0.60 gpm/sq.ft @ all room
>spacing: 100 sq.ft.
>Foam system: AFFF for 30 minutes
>500 gal hose stream
>Water demand 1 hr.

What can I do?
>
>I have a 2500 gpm @ 145 psi pump with a 200,000 gals tank.
>
>Regards!
>
>       
>
>
>
>