Gerzayn:

I would firstly determine if these are miscible or not.
     Get samples, at least 100 mL, and mix with water; observe and decide.
    If these are pure oils and extracts, they will be immiscible.
    No way of knowing the oil/extract concentrations unless you ask or
obtain samples.
    Flammable liquids presented as pure oils or extracts in plastic
containers are a REAL fire hazard.
    I am not looking up the exact protection criteria, so I don't know
precisely, but it will be serious.

Miscible liquid protection is usually a bit downgraded from that for
immiscible, if that is what
     0.6 gpm/sq. ft poses as.

Get the best quality foam that you can.  Citrus oil probably has acetates,
which are polar.   If there
     are a lot of acetates, you are going to want to deliver the foam onto
the surface as gently as you
     can.  That means your kind of screwed for optimal "soft-application"
from an automatic overhead
     discharge system.  Specify  a QUALITY alcohol-resistant foam.  A
quality foam can last 20 years, and knock down a pool
     fire with no more than 0.1 gpm/sq. ft.  Include in the bladder tank
capacity, half again as much
     foam as prescribed  for extinguishment, to control the room during
overhaul.

I would also specify at least a couple a 100-lb dry chemical extinguisher.
 Otherwise, if it is a spill fire
    without dry chem, you may be waiting until the upper containers burn
down before the foam starts to work.

I would have a full forward-flow test header, and a drainage and clean-up
plan.


Segue FM, tienen la voz.


Scot Deal
Excelsior Fire Engineering
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to