If this is an FM Global insured property, the owner or engineer of record 
should have submitted this project to them for review.  See if it has been 
reviewed by FM Global and if there has been a review letter issued.  That might 
give you some guidance for design.  

First you need to ask for Material Safety Data Sheets (MSDS) which will define 
the miscibility of the materials.  These sheets will also provide recommended 
fire suppression data, although you cannot always apply what they may indicate 
since most of the time they are referring to manual fire fighting measures.

Certain materials of certain quantities are not to be stored within a building 
and must be stored in a separate structure away from the main occupied 
building.  This here in the States is dictated within the Building Code.  

An architect should have known of these materials and should have designed a 
building with suitable rooms which would meet code and FM Global requirements.  
If this has not been the case then there are other problems beyond trying to 
configure a sprinkler protection plan.

So after determining the miscibility issue, you should ask the architect how 
his location of a storage room within the building meets code.

He may need to revise his design.


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, May 31, 2011 8:43 AM
To: '[email protected]'
Subject: Close head sprinkler with foam for flammable liquid

>
>Hello Folks.
>Here in Monterrey Mexico we are designing a sprinkler system for a
>flammable liquid storage inside cut-off room. The design should be FM
>Global approve. And I want you to help me with the design
>criteria/specification. I want to use a close head wet sprinkler system
>with foam AFFF.
>
>Description:
>Flammable Liquids in Plastic Containers
>Container size: less than 14 gal.
>
>Storage Arrangement: Palletized only
>Roof Height: 15'
>Flash point:
>       Lemon oil: 125ºF
>       Vanilla flavor: 64.4ºF
>
>
>Searching on FM DS 7-29, Table 15, less than 200ºF, inside cut-off, not
>miscible, cut not be protected. But in the same table if I get it as
>miscible, I found:
>K11.2 QR
>0.60 gpm/sq.ft @ all room
>spacing: 100 sq.ft.
>Foam system: AFFF for 30 minutes
>500 gal hose stream
>Water demand 1 hr.

What can I do?
>
>I have a 2500 gpm @ 145 psi pump with a 200,000 gals tank.
>
>Regards!
>
>       
>
>
>
>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to